I've got an issue with a FactoryTalk SE application I'm currently working on. I've got a CompactLogix Processor (1769 L35E) that will monitor some temperatures. In FactoryTalk Studio I've configured my RSLinx Enterprise server and HMI Server to support alarms and events.
I've created two ALMD instructions in the CompactLogix for testing. I can create numeric displays in the HMI to show that the InAlarm status is going from 0 to 1 when I toggle some input bits on the same rung as the ALMDs.
However, when the alarm becomes active the banner never displays this change, i.e. it continues to show "Waiting for Alarm Events"
It seems that the shortcut to the CompactLogix is working fine since I can see changes on the PLC tags on the HMI. However the Banner does not seem to be recognizing the alarms. Also, when I try to subscribe to events in the property tag of the banner I can browse the areas of my application but when I try to browse the event sources, I can't see anything pop up in the explorer window. I would greatly appreciate any help that anyone might have. I've attempted to follow all the set up in the online books included with FT View Stuido and the Alarm and Event Setup Guide.
Thank you for your time.
I've created two ALMD instructions in the CompactLogix for testing. I can create numeric displays in the HMI to show that the InAlarm status is going from 0 to 1 when I toggle some input bits on the same rung as the ALMDs.
However, when the alarm becomes active the banner never displays this change, i.e. it continues to show "Waiting for Alarm Events"
It seems that the shortcut to the CompactLogix is working fine since I can see changes on the PLC tags on the HMI. However the Banner does not seem to be recognizing the alarms. Also, when I try to subscribe to events in the property tag of the banner I can browse the areas of my application but when I try to browse the event sources, I can't see anything pop up in the explorer window. I would greatly appreciate any help that anyone might have. I've attempted to follow all the set up in the online books included with FT View Stuido and the Alarm and Event Setup Guide.
Thank you for your time.