Micrologix 1200 after power failure
e27978
Sep 2006
washington pa
35
I have a microligix 1200 processor for some valve control Im trying to stop it from powering up the outputs that were on prior to power failure on start I want it to execute the program as if it were just loaded checking input conditions to prevent all the valves from opening at one time when power returns can this be done through processor status file I tried changing the mem module bits but it did not change any help would be appreciated Thanks
You will probably have to deal with the logic itself. S:1/15 is a 'First Scan' bit and can be used to preset conditions on a power-up or program to run transition.
You may want to also research using "seal-in" logic versus Latch/Unlatch. I'm making an assumption here without seeing your code.
More suggestions may be provided if we can take a look at your program. Can you post it?
That is a good point. Real world Outputs should almost never be latched. Internal Bits can be latched, and then buffered with other conditions to decide if an output should go true. Only you know the specifics of your machine, and there exceptions to ever rule. An MCR Relay with a reset that kills all Output Power is a must on machines where un-commanded restart could cause machine damage or personnel injury.
Stu......
Hi I have a 1762-L40BWAR that I use for my central heating. I had a wiring fault which shorted my 24vdc input supply and now wont go, no lights or...
2,466
i have a micrologix 1200-L40BWA. im trying to power it up. According to my research. The VAC L1 is connected to the Hot(black) wire. VAC Neut is...
8,050
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
650
I have a MicroLogix 1200 that has an 8 input and a 16 output. Every 6 months-year I get a fault and when online go to error it is something like...
506
Have a bad output on a Micrologix 1200. Moved wire over to an available output, changed program to associate with new output. downloaded program...
753