Hi all,
I have an analogue input on a Schnieder Twido PLC.
The sensor measures distance and has a range of 100mm
It seems to only start working at 55mm away and reaches full range at approx 155mm.
So from 55mm I get 0(4mA) and at 155mm I get 4095(20mA)
My simple formula was z =(measured value 0-4095)
(z x 100) / 4095 this gives me a 0 to 100 value call it Y.
Y is its inverse so I have 100 - Y.
This seems to work but on different sizes i need to recalibrate and end up 80-Y or 85 - Y.
The formula is not right somehow although it seems logical to me - i have definitely missed the plot I wish the Twido had scaling.
Any mathematicians available ??? :unsure:
Hi!
Basic scaling methos is to use formula y=kX+b which you already have used, but take a look to thread http://www.plctalk.net/qanda/showthread.php?t=23382&highlight=EU and read Tom Jenkins reply to threat.
It's is also maybe better if you reconfigure twido analog module to use raw data values from 0 to 10000 (4
mA =0%, 20mA=100% ) instead of 0-4095. (You can use different raw data values to analog modules if you right mouse click above analog module and select configure => Range = custom...)
It's more easier to understand raw data values 0-10000 than 0-4095, when you use math in twido and you can see better were the error to scaling happens...
Thanks Lare
Just after the post i found out about the custom scaling I was going to use 0 to 100. But I think you are right 0 to 10000 is better.
This gives me a nice resolution to 2 decimal places.
Dear sir,
I am facing the following communication problem in twido plc please help me.
when i am going to communication through ethernet then it saying
communication error,Check communication parameter,network cable,configuration and controller supply.
But i have changed the cable but same problem i am facing.
hi all i have a problem with my twido plc i have a 3 analog input . 2 tempreture and one humidity.so i choose a analoge input modoule 4lt with 4...
2,842
79
Hi guys!! I'm New here and new with this type of plcs i have TWDLMDA40DTK and i need to get a copy of the program and i don't have an original...
714
Dear friend, how to read the input register (3xxxxx) of device from twido plc. i have tried the comm macro but it always read the holding register...
1,587
Good, how do I control through an Analog output of a valve, that is, open the valve from 10% to 10% until it reaches 100%, and then close it...
2,262