I have a serious problem here with two PLCs , S7-400 and S7-200. The problem is, I have a single sensor which I need to connect to both 400 and 200 CPUs. Unfortunately I have no possibility to make a network because 400 DP and MPI ports are already reserved for communicating with other PLCs and the port on the 200 is reserved for a HMI. in other hand, I have no access to any hardware module in the jobsite. I thought I can import the analog signal to s200 and send it to the s400 using the analog output card (232-0Hd22). But I don’t know if it’s possible to use an output module on the s200 as an input for an input module on a s400. Please help…
By the way, the connection on the S200 output includes 3 terminals (M0 V0 I0) but the analog input card on the s400 includes only 2 wires (A+ A-)
Dear RheinhardtP
thank you very much for your kind reply. unfortunately I have no access to any hardware to add. i was wondering if i could find a way to figure it out using existing hardware.
please comment which wan is doable from your point of view? using a single sensor for two PLCs or using one PLCs output as the other's input?
thanks again
I don´t know which S7-400 analog Input card are you using. You should not have a problem in making the connection. Just connect the I0 to MI+ and the M0 to M-. You just have to make sure the "Measuring range module" in the S7-400 analog card, is set not to power the current loop (4 wires).
Hi, I am working on a project with Delta PLC for the first time. I want to connect a Sinking analog sensor (4-20 mA) to a Delta analog module...
1,666
Hello guys, I have a pressure sensor with 0-10 control and 0-600 bar range. how can i read from it the signal and transfer it to bar and stored...
20
7,767
Hi, Calculation of voltage drop of a 2 wire transmitter connected to plc AI is pretty simple and straight forward. My Question is could you...
2,158
I have a very simple program which is run by a 2080-LC10-12QWB Micro810 PLC connected to a single sensor. The sensor has two outputs, one which...
4,883
Hey, We have a 3-wire 4-20mA sensor that is connected to a display like this Now i need to connect this to a siemens ET200S analog input...
2,946