3-wire 4-20mA - connect in line with Analog input and dispaly
ason
Oct 2005
Home
317
Hey,
We have a 3-wire 4-20mA sensor that is connected to a display like this
Now i need to connect this to a siemens ET200S analog input module
think to use
6ES7134-4GB11-0AB0 2AI, I, standard, for 4-wire
is´t possible to connect the analog input inline with sensor and display
something like this?
pin on analog input
1 M+
2 M-
In most cases the answer is no because what you suggest will change the resistance of the load on the sensor.
The preferred way to do it is to add a splitter that give you two 4-20ma outputs or change the display to one with a 4-20ma output.
The cheap and dirty method is to wire your PLC input in parallel with the display and set the module of 1-5vdc.
as long as you 4-20mA loop total resistance is below 500ohms, it should work if you wire devices to series.
Current transmitter can drive usually at least 500ohms, but it depend of manufacturer and device etc.
You can use signal splitter or analog output of PLC for display also. Signal splitter cost maybe more than ET200 analog output card.
I've seen it done many times. About three 4-20mA inputs per 4-20mA output. It depends on the devices and the resistance in the wires.
For instance if the current loop is supplied by 24V and each devices drops the voltage about 5V you could put 4 devices in series.
PS. Which 4-20mA sensor are you using?
There is no need to guess on this. Look up the max load/burden on the transmitter. Add up the total resistance of all the devices in the system. If the total is less than max allowed you are OK.
One caution: loop powered indicators use an internal diode to create a voltage drop and power the electronics. At low outputs (i.e. 4 mA) this diode can look like a very high resistance. Check it out carefully if you have loop powered devices in the circuit.
I'm probably going to be called stupid for asking this. I have only ever used 2 wire sensors. we would connect one wire to 24 dc+ and the return...
41
7,199
Hi, May i know the how to know the minimum voltage to drive a analog input card. I'm connected to 4-20mA channel for 4 wire, supply voltage from...
6,652
I have a SLC 500 PLC with NI4 analog input card. I am using two 4-20mA signal coming from an RTD transmitter. The overall length of the cable is...
5,233
Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
265
Hi everyone, I need some help I new with omron plc. I using plc CP1L. When I do the program it's good and the plc is function as program. But when...
86