Contollogix Remote Rack Status
mcalidl
Aug 2006
Birimingham, AL
50
I know there is a way to check the status of a remote i/o rack over ethernet in the controllogix, I'm just not sure how yet. Here is what we have: Rack with Processor and 1756 ENBT card and then a remote rack with an ENBT card. I am looking for a way to alarm if the remote rack drops of the network.
If you are using Rack Optimization for the modules on the remote rack, you can use the SlotStatusBits DINT to get information about the modules.
1=connection lost, 0=connectiion established
This DINT is available at the top level of the ENBT in the remote rack. For example, if the ENBT has the name "RACK01", it would look like this.
Rack01:I.SlotStatusBits when viewing in Controller Tags.
Yes...The CIP connection (which is how the I/O is communicated between the racks) between the local rack and the remote rack would be lost and the values in this DINT would be updated to reflect this.
Please note that this will only work if the module is set for RackOptimization. The value will be bogus if it is anything else. Also, it is only an indication of the connection to the module and tells you nothing about any faults or misconfiguration on the module. If you need additional information, you will need to use the GSV method already mentioned.
Ok. Right now the SlotStatusBits DINT has hex value FFFF_FF0F while everything is OK. What value should I look for? There is nothing in Slot 0, ENBT in Slot 1, and I/O cards in Slots 2-7, and Slots 8 and 9 are empty in a 10 Card Rack.
I can't tell you what the number should be until you give me more details on how the remote IO is configured in RS5000.
Create a message instruction and in the configuration use the following:
Message type = CIP Generic
Service Type = Get Attribute Single
Service Code = e
Instance = 1
Class = f6
Attribute = 2
In the destination, create a DINT tag call it say LinkStatusWord
In the communication type the name of the ethernet card in the remote rack (e.g - EB_01)
Bit 0 is the link status in the LinkStatusWord ( 1 = Active ; 0 = Inactive)
Bit 1 is module duplex mode ( 1 = full duplex ; 0 = Half Duplex)
Bit 2 to 31 are reserved.
Use Bit 0 as you indicated for the connection.
I use the CIP MSG for communications modules, and GSV for IO modules that are in the IO tree.
Then I can use this information to determine a "rack fault" alarm, and/or loss of comms alarm.
Can't install firmware higher than v29 on an L82E CPU Fails at end when polling for power up AB-CIP pop-up reads 'Failed to communicate with the...
2,373
I am looking for a strictly objective comparison of these two platforms. What are the differences; communication, modules, tags, anything and...
4,580
I have a 1756-L55/A, Rev. 11.25 that lost it's program while running. When I got to the panel, the BAT LED was dark and the OK LED was solid red...
2,751
We have CLX system with redundancy and control net. When we inject a 4-20 signal into an input, we are losing 1mA. We have verified out source as...
3,682
Hi, I've been reading this post for a while now and have picked up a lot of great tips. Now I need some serious help! My company wants to convert...
20
8,730