Alcoa Tech said:I understand what you mean. I've read that a conversion from PLC 2 to PLC 5 then to CLX is not very good. Do you know if the get and put command could be converted? What about block transfers? If I have to redo those it would seem easier to start from scratch. I know starting from scratch on the program would be better in the long run because the program should be much cleaner. I really would like to save some time. The program currently has almost a 1000 rungs. I think some of those would go away but there still would be a lot left.
GET and PUT are equivalent to the MOV instruction. The MSG instruction will simulate the BTR and BTW with the same parameters as the original BTR and BTW
example of a BTR to an analog input card from a PLC2 to Clgx conversion