Hi. I am trying to reproduce a customer issue with a multi rack SLC configuration. I have multiple SLC racks (2 4 slot racks with 1746-P2 power supplies, 3 io modules per rack and a 5/04 and a 5/05 cpu respectively). So if my understanding is correct I would just need an expansion cable to connect the racks? Is this correct, or am I missing something?
you can connect the racks several ways.
1. rack connection cables.
2.dh+
3. remote I/o
devicenet, control net???
what does the customer have?
exact rack details.
do you have his program?
if yes, look at the configuration.
can you get the program?
what is his issue? maybe someone here has had the same issue.
james
I thought the rack connection cable was for expanding the number of I/O slots only.
Not for connecting 2 rack with different CPU
Someone correct me if I am wrong.
Correct. The cable connects the "backplanes" of two chassis to expand the number of slots. It essentially treats the two chassis as one big chassis. It cannot be used to connect controllers in two separate chassis.
With two 4-slot chassis you would have slot 0-3 in the first chassis and slots 4-7 in the second chassis. A controller can only reside in slot #0 so you cannot have a CPU in the second chassis.
The SLC 5/04 has DH+ and a serial port while the 5/05 has Ethernet and a serial port. There isn't a real easy way to connect those two. However, there is an adapter that can use the serial port of the 5/04 to connect it to Ethernet.
OG
2.dh+
3. remote I/o
exact rack details.
james
Hi James,
Thanks for the swift reply. I do have the customer project. When I open his .RSS file and go to the I/O configuration I see 2 13 slot racks configured with I/O.
What the customer is reporting is that with our AB Ethernet driver they are able to read tags from I/O points in the first rack, but when they try to add tags referencing I/O in the second rack all tags have bad quality. So I need to use the rack connection method to not introduce additional variables and insure similar addressing. So here is what I have for hardware in front of me
Rack 1 (4 slot with 1746 P2 supply)
SLC 5/04
blank
1746-ib16
1746-ia8
Rack 2 (4 slot with 1746 P2 supply)
SLC 5/05
1746-ia8
1746-ov32
1746-ox8
Is my understanding correct that I could just get the rack expansion cable (p/n currently unknown) and connect these 2 racks and configure as a 2 rack device in RSLogix 500?
Sorry for the misunderstanding. I am not trying to connect multiple CPU's in 1 expanded rack. My understanding is this is only possible with Controllogix devices. I was simply stating what I had for hardware at my desk in its current configuration state. I plan to pull the 5/04 and use the 5/05 so I can be connected with RSLogix as I cant use my u2DHP adapter while testing with our drivers as they use the same Virtual COM port.
Yes, but remove the cpu from the second chassis. Note too that the expansion cable cannot be very long. Three cables are available.
1746-C7 is 6 inches
1746-C9 is 36 inches
1746-C16 is 50 inches
OG
** edit ** You can change the virtual COM port settings of the U2DHP.
you are using the term bad quality.
does this mean they are seeing the bad quality tags in a SCADA system or in the RS500 Program??
1746-C7 is 6 inches
OG
thank you for for the part numbers, much obliged!
yes I can change the COM port, but we use the same low level drivers as Linx does so I cant have both connections through the u2dhp.
bad quality in our DA quick client that we provide for test purposes. all tags are correctly defined on the device in RSLogix 500 with a valid configuration that is in production.
very strange... (obviously)
the I/O in the expanded rack should no be different than the I/O in the rack with the CPU.
I assume the the customer's PLC running with no faults???
the I/O in the rack matches the configuration, according to information provided to me. the process being controlled is a dewatering plant and they are in production so i am inclined to believe this information is correct.
correct he is running with no faults. I am not responsible for the customer project, I am simply trying to create a scaled down analog in my lab so I can determine if there is an issue with our driver when reading tags from I/O cards in Rack 2.
there is a program i used only a few time called RSLogix Emulate 500.
This only emulates your SLC program on your PC.
With the SLC500 you a cannot simulate a program in the Processor.
the Processor needs the correct I/O cards physically installed otherwise it will fault.
Hi Fella's, Just wondering if anyone else has noticed that the backplane clips are missing on SLC A13 expansion racks these days? These clips...
2,714
I used up my last new Allen-Bradley SLC 5/04 controller. Does anyone have info on a good reliable place to get a new one for a decent price, or...
543
Is this possible to do on the SLC platform? The reason I ask is I would like to upgrade from a 5/04 to a 5/05 in one machine to get the use of...
1,741
HI guys, wondering if anyone has used a 1746-C9 rack extender cable to connect 2 (or more) SLC 5/05 racks when upgrading the SLC to compact logix...
3,304
All, Thanks for any help. I am currently changing out an 1747-L543 processor over to an 1747-AENTR card so that I can now run this rack from an...
2,143