Can't establish communication

Hi. I have a PanelView Plus 600 panel and a Honeywell C200 controller. The task is to connect them for joint work. FTView Studio 6.10 software is installed to work with the panel, but RSLinx Enterprise does not define a Honeywell controller. There is RSLinx Classic for which EDS files for Honeywell equipment are installed. It sees and recognizes the controller. But there is no way to put these EDS files in RSLinx Enterprise. Any ideas how to get out of this situation?
  Reply With Quote
Old February 7th, 2018, 04:49 PM   #2
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 2,409
Welcome to the forum!

To use a third-party controller with a Panelview Plus, you need to use the included Kepware OPC server.

You will need to flash the firmware on the HMI, and when you do, select the relevant Kepware drivers to be loaded onto the hardware. Then you'll need to configure the tags in Kepware to be used in FTView Studio.

That's the short version - now that you know what to look for, give it a try and let us know if you need more help!
  Reply With Quote
Old February 8th, 2018, 01:34 AM   #3
Kaktus33
Member
Poland

Kaktus33 is offline
 
Join Date: Feb 2018
Location: Gonduras
Posts: 3
Quote:
Originally Posted by ASF View Post
Welcome to the forum!

To use a third-party controller with a Panelview Plus, you need to use the included Kepware OPC server.

You will need to flash the firmware on the HMI, and when you do, select the relevant Kepware drivers to be loaded onto the hardware. Then you'll need to configure the tags in Kepware to be used in FTView Studio.

That's the short version - now that you know what to look for, give it a try and let us know if you need more help!
Thanks.
I thought about it, but in the firmware for HMI there are no drivers for the Honeywell C200 controller and Kepware Enterprise also does not contain the necessary drivers. The problem is that this equipment is not supported and how this can be changed is not clear.
  Reply With Quote
Old February 8th, 2018, 11:02 AM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 13,618
Honeywell C200 controllers share some hardware with Rockwell Automation ControlLogix because of the joint venture for process control applications more than fifteen years ago. Rockwell called it ProcessLogix, Honeywell called it PlantScape.

I don't know if FactoryTalk View (and thus the PanelView Plus 600) will work with any of the Honeywell operating system objects.

I recommend researching support in the C200 controller for Modbus/TCP protocol support. The PV+600 does support Modbus/TCP via the Kepware driver suite.
  Reply With Quote
Old February 9th, 2018, 01:31 AM   #5
Kaktus33
Member
Poland

Kaktus33 is offline
 
Join Date: Feb 2018
Location: Gonduras
Posts: 3
Quote:
Originally Posted by Ken Roach View Post
Honeywell C200 controllers share some hardware with Rockwell Automation ControlLogix because of the joint venture for process control applications more than fifteen years ago. Rockwell called it ProcessLogix, Honeywell called it PlantScape.

I don't know if FactoryTalk View (and thus the PanelView Plus 600) will work with any of the Honeywell operating system objects.

I recommend researching support in the C200 controller for Modbus/TCP protocol support. The PV+600 does support Modbus/TCP via the Kepware driver suite.
Thanks, I'll try to work in this direction.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
PanelView Plus ---> SLC L551 Ethernet Communication Issues celichi LIVE PLC Questions And Answers 17 May 3rd, 2016 12:40 PM
How to establish communication between MVI69-GSC with Parker HPC Servo drive AB2005 LIVE PLC Questions And Answers 0 September 17th, 2012 07:58 AM
S7 313C communication port repair sttchui LIVE PLC Questions And Answers 1 March 25th, 2008 04:14 AM
How to establish communication between SLc 5/03 and multiple Modbus devices M. HASSAN LIVE PLC Questions And Answers 6 August 25th, 2007 04:14 PM
OPC Communication ikon2018 LIVE PLC Questions And Answers 0 June 21st, 2005 06:47 AM