Vacuum switch compatible with Chlorine Gas

We got a quote from a vendor of some chlorine equipment but it is pretty expensive. ($525) It appears to be a UE brand vacuum switch with an isolator diaphragm. They don't tell us exactly what materials they're suing for this assembly.

I just wanted to see what others have used or would recommend to monitor the presence of vacuum in the line that pulls chlorine gas through a flow regulator. The customer has had an issue in the past with the ejector pump failing to run or other issues that might cause a loss of vacuum and we would wire a contact from a vacuum switch to a PLC input to generate an alarm if it opens. It would be good to have an adjustable switch. I know from experience that chlorine and copper do not get along well, and the same appears to be true for stainless steel.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old June 22nd, 2018, 10:38 AM   #2
geniusintraining
Lifetime Supporting Member + Moderator
United States

geniusintraining is offline
 
geniusintraining's Avatar
 
Join Date: Jun 2005
Location: SC
Posts: 5,464
Quote:
Originally Posted by OkiePC View Post
We got a quote from a vendor of some chlorine equipment but it is pretty expensive. ($525) It appears to be a UE brand vacuum switch with an isolator diaphragm. They don't tell us exactly what materials they're suing for this assembly.
Hi Paul

I dont think 525 is that bad, any EX or corrosion resistant is not going to be cheap, the body should still be 316 even if it has a isolator built in, I have used Copal in the past and they held up well

http://www.netmotion.com/graphics/ps/pa850.pdf

Your supplier is going to mark everything on these and most of my issues were lead times, we used a company in NC http://www.statesvilleprocess.com/ they made a lot of their own products for temperature and the quality was great... but they also supplied a lot of other brands
__________________
www.PLCCable.com PLC Communication Cables, PLC Trainers, Fluke Meters, MicroLogix, ControlLogix, Siemens, Allen Bradley and more... all your automation needs... ((NEW)) After Market 1784-U2DHP Allen Bradley USB to DH+ and Gateways
  Reply With Quote
Old June 22nd, 2018, 10:50 AM   #3
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,781
Thanks Mark! The lead time is 5-6 weeks too. The vendor who gave us the quote is a good one of ours, so we may just use them, but I want to weigh other options. After digging deeper, he does spell out more of the details in the price quote, like the UE switch being epoxy coated, and the material in the isolator plus that it is filled with a "halocarbon" fluid. I think that is what drives up the price, plus they probably have to calibrate it after assembly.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old June 22nd, 2018, 06:53 PM   #4
Saffa
Member
New Zealand

Saffa is online now
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 845
My general approach to chlorine gas systems is to install a flow switch on the carry water pump before the gas injector. My experience has been that vacuum regulators rarely fail; it tends to normally be the pump or lack of water. Our systems always have a standby cylinder with auto changeover anyway. I've never monitored vacuum pressure before.

Is there a chlorine residual monitor down stream of the injection point? That's always a good catch all for injection issues.
  Reply With Quote
Old June 23rd, 2018, 03:47 PM   #5
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,781
Since this is a wastewater application, they do manual tests for chlorine residual downstream, and they should find none since there is also sulfur dioxide injection to eliminate CL2 later in the process.

The original set up did have a vacuum switch, but it had failed (cracked diaphragm) many years ago and we have recently added chlorine flow pacing with electronic analog regulator to the system. They were wasting a lot of chemical running it at a level high enough for peak flow rates...

I thought of monitoring water flow, but there are about two things that could go wrong and cause a lack of chlorine even if water is flowing, but if there is a vacuum, basically the only thing that could go wrong from there is an empty bottle. They do have a mechanical automatic change-over valve on the bottles.

I will probably just go with the $525 switches since the guy who quoted them sells us CL2 equipment and will stand behind his line...I just wanted to see what others might recommend before I spend that much other people'$ money.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old June 24th, 2018, 02:31 AM   #6
Saffa
Member
New Zealand

Saffa is online now
 
Join Date: Feb 2012
Location: Bay of Plenty
Posts: 845
Ah, wastewater.

Not something we chlorinate here!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Problem with BTW & BTR in PLC-5 Gsquare LIVE PLC Questions And Answers 38 January 26th, 2015 05:45 AM
Help with Micro 1000 program GMc LIVE PLC Questions And Answers 60 August 4th, 2007 02:58 PM
Control Logix ENET & Hirschmann switch Vlad_M LIVE PLC Questions And Answers 4 December 1st, 2004 06:55 AM
Vacuum thermocouple integration to PLC grignon LIVE PLC Questions And Answers 1 April 26th, 2003 07:58 AM
Normally open or closed or... Phil Melore LIVE PLC Questions And Answers 15 February 3rd, 2003 07:14 PM


All times are GMT -5. The time now is 06:45 AM.


.