Greetings,
Can a Single Pole Double Throw snap switch be furnished such that it actuates on low level or high level, but remains in "neutral" state when in a dead band region? We need a switch with two normally open contacts, with one contact closing on low oil level condition, and the other contact closing on high oil level condition. We want the switch contacts to remain open when the level is in between the two trip points.
Perhaps I need (2) SPST switches for this arrangement.
This is a Magnetrol switch.


Any thoughts?
Thanks,
EE
  Reply With Quote
Old October 19th, 2020, 01:42 PM   #2
drforsythe
Member
United States

drforsythe is offline
 
Join Date: Aug 2016
Location: Metro Detroit, Michigan
Posts: 123
This will not answer your question, but I will describe my "best practice".
For critical operations, like oil level, I prefer to have a signal when the level is in a "normal" position. Both low and high level switches would be on and sending a signal to the controller or indicator lamp. If a low or high condition occurs, then that input (or lamp) would turn off. This way, if a wire comes loose or is somehow disconnected, it will alert you that the level is not normal or the switch is not working.
I thought companies like Magnetrol had multiple switch and level options in the same level device. It has been many years since I spec'd one, though.
  Reply With Quote
Old October 19th, 2020, 01:44 PM   #3
Bob O
Member
United States

Bob O is offline
 
Join Date: May 2003
Location:
Posts: 1,849
Have you contacted Magnetrol and asked this question?
__________________
There Is A Frost Advisory...GBR!
  Reply With Quote
Old October 19th, 2020, 02:42 PM   #4
ndzied1
Lifetime Supporting Member
United States

ndzied1 is offline
 
ndzied1's Avatar
 
Join Date: Aug 2002
Location: Chicago, Illinois
Posts: 2,553
The traditional definition of a "snap action" switch, while not an official technical term, is that it changes, "snaps" from one side to the other. So that would rule out a 3rd position.
__________________
nOrM
======================
nOrM=Norman Dziedzic Jr.
I've never been to China but my phone has.
  Reply With Quote
Old October 19th, 2020, 03:43 PM   #5
Gene Bond
Member
United States

Gene Bond is offline
 
Join Date: May 2004
Location: Indianapolis, IN
Posts: 493
If you want deadband between the contacts, you'll likely need 2 switches, since most all switches are form C, not 2 independent contacts....
  Reply With Quote
Old October 20th, 2020, 12:12 AM   #6
janner_10
Lifetime Supporting Member
United Kingdom

janner_10 is offline
 
Join Date: Dec 2014
Location: Tewkesbury
Posts: 1,103
I would be wanting the switch closed between the high and low levels. If your level is good and the cable is cut, you have no feed back and nobody will know.
  Reply With Quote
Old October 20th, 2020, 09:32 AM   #7
saultgeorge
Lifetime Supporting Member
United States

saultgeorge is offline
 
saultgeorge's Avatar
 
Join Date: Jul 2015
Location: Detroit
Posts: 358
' I would be wanting the switch closed between the high and low levels. If your level is good and the cable is cut, you have no feed back and nobody will know. '

+1. This is known as "failsafe" method of wiring alarms and statuses. At my last job with an integrator, it was a requirement from most of our customers, and I wired and programmed failsafe even when it wasn't a requirement.
__________________
"It's better to be on the ground wishing you were flying than flying wishing you were on the ground."
  Reply With Quote
Old October 20th, 2020, 09:43 AM   #8
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 3,125
I'm confused. Level switches trip at a given level and have an output to reflect the status of the level.


If you want a low level switch AND a high level switch you have two level switches, one for low level, one for high level and you connect them as needed.


What sort of single level switch detects and signals both high and low level that brings up your question?
  Reply With Quote
Old October 21st, 2020, 03:41 AM   #9
rkicklighter
Member
United States

rkicklighter is offline
 
Join Date: Jan 2007
Location: Statesboro, GA
Posts: 108
Quote:
Originally Posted by drforsythe View Post
This will not answer your question, but I will describe my "best practice".
For critical operations, like oil level, I prefer to have a signal when the level is in a "normal" position. Both low and high level switches would be on and sending a signal to the controller or indicator lamp. If a low or high condition occurs, then that input (or lamp) would turn off. This way, if a wire comes loose or is somehow disconnected, it will alert you that the level is not normal or the switch is not working.
I thought companies like Magnetrol had multiple switch and level options in the same level device. It has been many years since I spec'd one, though.
We use level switches on some of the Navy ships I have designed PLC control systems for that function in exactly this manner. They are a three-wire switch and when in normal operating level both outputs from the switch are "High", if the level goes too high or too low then that side of the switch goes "Low".

We call them "Alarm on Zero" since they are failsafe.

I don't spec the switches but if I remember correctly there made by GEMS.
  Reply With Quote
Old October 21st, 2020, 07:08 AM   #10
ndzied1
Lifetime Supporting Member
United States

ndzied1 is offline
 
ndzied1's Avatar
 
Join Date: Aug 2002
Location: Chicago, Illinois
Posts: 2,553
Quote:
Originally Posted by danw View Post
What sort of single level switch detects and signals both high and low level that brings up your question?
This sounds more like an analog level sensor with multiple switching outputs.
__________________
nOrM
======================
nOrM=Norman Dziedzic Jr.
I've never been to China but my phone has.
  Reply With Quote
Old October 21st, 2020, 08:26 AM   #11
drforsythe
Member
United States

drforsythe is offline
 
Join Date: Aug 2016
Location: Metro Detroit, Michigan
Posts: 123
rkicklighter- GEMS is the company I was thinking of, as well. In my response, I stated "Magnetrol", but GEMS is the company I was thinking of. I just did not remember the right company name. Thank you for the info.

If you go to the GEMS website (gemssensors.com), you can search in their Multi-Point Level Switches category.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
24VDC Snap switch Rson LIVE PLC Questions And Answers 6 May 26th, 2020 05:43 PM
Switch in combination with a timer pdupreez LIVE PLC Questions And Answers 2 February 21st, 2014 03:08 PM
Switch works, NOT! Narlin LIVE PLC Questions And Answers 17 January 19th, 2014 11:54 AM
Machine Guarding - Deadman Switch khurley LIVE PLC Questions And Answers 9 January 31st, 2007 07:54 AM
Control Logix ENET & Hirschmann switch Vlad_M LIVE PLC Questions And Answers 4 December 1st, 2004 07:55 AM


All times are GMT -5. The time now is 09:33 PM.


.