I see how the safety test pulse/test output works but what makes a safety input a safety input? We use safety pulse test/test outputs for push buttons and contact closures and safety inputs for proximity sensor inputs and such. I just don't really see how a safety input is any better than a standard input other than the safety processor having the companion processor. Could someone elaborate on this?
Safety input card can have tests and diagnostics of the input card. eg. it will disconnect the input, connect it to 24V and make sure it gets the expected result.
Safety input card and safety sensor will have a 'probability of failure safe condition' and 'probability of failure unsafe condition' that can be used for safety reliability calculations.
Safety input card can have two channels for the one input for comparison.
If using a semiconductor input, (ie. not relay contacts) the card can monitor for: short circuit to 0V/24V and open circuit.
Also, there are administrative controls so that additional procedures must be followed for any modifications involving a safety input.
Hey everyone, I have a problem that is the CROUT keeps faulting out with a "16#5003 20483 Feedback 1 and Feedback 2 turned ON (1) unexpectedly."...
1,294
Good Afternoon , I'm thinking of using Allen-Bradley 440G-T27240 Locking Switch, 24V AC/DC, Solenoid. Can you use the MSR-127TP with this ...
1,076
Dears, I have problem with 5069-obv8s, trying to use it for a first time just to power relays. All outputs are in internal fault, even if their...
4,672
Good Evening , I have a Guardmaster Safety Relay I have 14 vdc on S12 (Safety Input for IN1 Channel 1) and on S22 (Safety Input for IN1...
3,557
Good Afternoon , We have a number of these Allen Bradley GuardMaster Safety Relays in the plant. We had a problem with a safety circuit...
1,952