Allen Bradley GuardMaster- Looking for internal workings of this Safety Relay
Aug 2016
Virginia
343
Good Afternoon ,
We have a number of these Allen Bradley GuardMaster Safety Relays in the plant. We had a problem with a safety circuit this morning. Would you folks have a link to some detailed internal diagrams showing the workings of the internal electronics ? The Rockwell website has a Block Diagram but it does not show much. The model I am working with is MSR 127RP ( 440R-N23134 110 vac Supply) and the MSR 127TP ( 440R-N23132 24 AC/DC ).
Also , these 2 operate the same , just the supply voltage is different , correct ?
Thanks so much,
It's been a while, but I *think* that the RP and the TP differ in their reset philosophy - one is automatic reset (i.e. resets as soon as the safety channels are healthy, provided the reset loop is made) and the other is monitored manual reset (i.e. must see safety channels become healthy and THEN the reset input turn on, and then off again).
The manual has some block diagrams of the internal workings, but it depends on how they're wired as they can be configured to work in a few different ways depending on how you connect the wiring. In general, they need to see both safety channels turn on at the same time (or within a certain fixed tolerance), and then the reset loop must be either already made or pulsed on and off to reset, depending on the outputs. When you operate the safety device (e/stop, guard switch...), both safety channels must turn OFF at the same time (or, again, within a fixed tolerance). If they don't, the safety relay will generally fault and will have to be power cycled to make it work again (some of them will work again if you release-press-release the e/stop again, and the inputs all turn on and off correctly again). I believe many of them will also fault and require power cycling if their output channels are detected to not switch on and off correctly, but I've never had one fail in this manner to be sure.
If you need more information, provide some more detail about the fault you experienced, and the symptoms you saw.
Team, I have had some issues with my MCR dropping. This is an issue that has been in 2 of my lines prior to me coming to this facility. The...
2,033
Good Evening , I have a Guardmaster Safety Relay I have 14 vdc on S12 (Safety Input for IN1 Channel 1) and on S22 (Safety Input for IN1...
3,567
376
Dear community, I am trying to find a tool for Allen-Bradley PLCs similar to SiVArch for Siemens PLCs to automatically generate faceplates and...
96
Hi everyone, new to forum. Since very long time i having issue with 1734-AENT module, after some period of time its keep stuck in error (simmilar...