Team,
I have had some issues with my MCR dropping. This is an issue that has been in 2 of my lines prior to me coming to this facility. The maintenance staff informed me that when they drop MCR, they do not get any alarms. They thought it was a problematic e-stop and would go giggle the wires until the MCR would turn on.... monkeys with hammers I tell ya...
I was able to catch this issue this morning when I came in to support start up. I let the maint staff do what they usually do, so as to get an idea as to what might be the problem. After they did their wire giggling with no resolution, I stepped in and started ohming out the system.
I was able to deduce that one of the control wires through the e-stop on one of the ops was having issues, upon opening up the e-stop box, there was in fact a terminal that was broke. Upon fixing the broken wire, we got MCR Power back.
Now that I have power to my line, I have a strong desire to not have to climb through these station boxes again.
The e-stop circuit is monitoring for a True value, which in turns drops MCR and throws an HMI Alarm for OP_XXX_ E-Stop, this is easy to find.
The guardmaster is not monitored, when we drop a connection in the line for the guardmaster, its all hands on deck digging through boxes to find the lost signal, as each station is daisy chained to the next.
I would like to monitor the output side of each station's guardmaster circuit.
I have fears that running a leg off of the output side of the circuit to the PLC will cause issues with the circuit. I have been told that there is a pulse modulation that the guardmaster pushes out and monitors on the feedback side that can get angry if you try to mess with the circuit.
Any advice, or things I should watch out for?
I have had some issues with my MCR dropping. This is an issue that has been in 2 of my lines prior to me coming to this facility. The maintenance staff informed me that when they drop MCR, they do not get any alarms. They thought it was a problematic e-stop and would go giggle the wires until the MCR would turn on.... monkeys with hammers I tell ya...
I was able to catch this issue this morning when I came in to support start up. I let the maint staff do what they usually do, so as to get an idea as to what might be the problem. After they did their wire giggling with no resolution, I stepped in and started ohming out the system.
I was able to deduce that one of the control wires through the e-stop on one of the ops was having issues, upon opening up the e-stop box, there was in fact a terminal that was broke. Upon fixing the broken wire, we got MCR Power back.
Now that I have power to my line, I have a strong desire to not have to climb through these station boxes again.
The e-stop circuit is monitoring for a True value, which in turns drops MCR and throws an HMI Alarm for OP_XXX_ E-Stop, this is easy to find.
The guardmaster is not monitored, when we drop a connection in the line for the guardmaster, its all hands on deck digging through boxes to find the lost signal, as each station is daisy chained to the next.
I would like to monitor the output side of each station's guardmaster circuit.
I have fears that running a leg off of the output side of the circuit to the PLC will cause issues with the circuit. I have been told that there is a pulse modulation that the guardmaster pushes out and monitors on the feedback side that can get angry if you try to mess with the circuit.
Any advice, or things I should watch out for?