I have 4 vfd's in total supplied from one largest vfd in system. The other three vfd's don't have connection to ac grid. These 3 vfd's are supplied from common dc bus. I don't understand exact reason why I must fuse each inverter dc input. Some documents say it is done for protecting vfd against overloads and some documents say it is for protecting other vfd's in case of short-circuit that may happen in any vfd. Short circuit theory seems logical to me but I can't understand the one says it is against overload since vfd output already protect itself from overloads and there is no connection at the front end of these drives. What is meant by overload then (they are supplied by common dc bus only)
Is there anyone who has comment on it ?
Thanks in advance.
 
When you have a converter, or several converters, feeding a common DC bus, that converter capacity ends up being much larger than a single smaller drive connected to the bus. That means the DC bus capacitance is much higher as well and the potential for destructive energy on the smaller drive is disproportionate to what the components inside of the inverter section are designed to handle. The high speed semiconductor fuses are needed therefore to limit the potential destruction and resulting collateral damage should something go awry. You can do it without them, but if one small drive goes bad, it will likely take out EVERYTHING on that bus. Fuses are cheap insurance.
 

Similar Topics

Hi everyone id like to start by saying im not a PLC programmer so my technical terminology is limited. i would like advice on what software is...
Replies
4
Views
297
Hi all. Please can anyone assist me with a Devicenet EDS File or link for a Numatics G2-2 solenoid valve bank. Need to do configuration on a...
Replies
3
Views
705
Hello everyone. I am working on a rebuilt AB-Ultra series drive (1998) and the firmware for the drive is needed to test and use the drive. I would...
Replies
0
Views
452
Hello everyone, We are trying to upgrade a GE FANUC 9030 PLC, but we are having trouble extracting the program from it. LogicMaster90 is able...
Replies
6
Views
1,305
Hi , Does anyone have any pdf or manual on the GEM 80 Gemlan T card Could you let me know Many thanks Mike
Replies
0
Views
397
Back
Top Bottom