Hi
The pump smart PS220 VFD has the ability to estimate pump flow based of pump characteristics and measured motor data.
The calculations requires BEP flow, BEP Power, pump rated speed and power at zero flow.
Does anyone know how this is done such that I can implement it on the PLC in those applications which doesnt use the pump smart VFDs?
Just finished an aeration control system using centrifugal blowers. Typically I use a loop with dissolved oxygen as input, and flow in scfm as output. This is an upgrade to an existing system. The existing system had surge, overload, design point, and a couple other points superimposed on an analog current meter. Plotted those points, and for the region of concern, it was fairly linear. So a simple y=mx+b works. Convert loop generated scfm target to current, and control inlet valve to blower to hit target.
This is crude, but effective.
So short answer, you need the pump curve. Current and speed feedback from drive, and probably discharge pressure to come up with a good approximation.
Of course you could put a flowmeter on the discharge side of the pump, and this all becomes academic.
Hope that helps!
It looks to me as if the fundamental calculation is simply the linear approximation that atc222 used for his blower. At the base speed they calculate using y = mx + b, with y flow and x power. The get the slope, m, from the two points of flow and power, and then calculate the intercept, b, from the power at zero flow. They then apply the affinity laws to correct for different speeds.
Some pump curves don't go back to zero flow. In that case you can take the power at the minimum flow given and calculate the intercept.
I'm a bit skeptical about the ±5% accuracy, especially at alternate speeds, since the basic pump curve is typically ±3% by itself and for some pumps the hp to flow curve isn't really a straight line.
There is a fifth parameter: the pump type.
Cf. https://www.ittproservices.com/ittg...roducts/Control Solutions/PS220/PS220_IOM.pdf page 19, item C.
Other items of note:
  • "complex algorithm" (pp. 18, 140)
  • "SmartFlow can have an accuracy of ±5% of rated flow at rated speed. This is made possible by conducting
    a SmartFlow Tune. The SmartFlow Tune is conducted against a closed discharge valve and will take no more
    than 35 seconds." (p. 31)
So a complex algorithm, plus an automated calibration, and they can get 5% accuracy.
It might be possible to calibrate your own pump and make a model from that plus some basic affinity laws.
I am a little confused by the "Efficiency" ordinate on the right hand side of the plot in the YouTube video.
Tom,
Any chance you could post links to the articles you’ve written? I’m currently living in the water/wastewater world, and I find on occasion I’m reinventing the wheel. Successfully, but I’d benefit from your knowledge.
Regards,
Andy
ps: Folks like you and Peter N. are great resources, and make this site worthwhile! Not leaving anybody out, just citing a couple examples.
Tom,
Sure thing! You can access books, articles, and white papers from my website:
https://www.jentechinc.com/publications.php
(And thanks for the kind words.)
I have an application where a user is driving a servo to two absolute positions repeatedly in a back and forth motion using MC_MoveAbsolute. The...
5,497
I work in rolling mill. Many ac motor drives are using in the mill. I have seen for ac motor current reference calculation mechanical losses are...
1,352
In historian, can I perform calculations on a recorded tag? Like the average value over time? Or timer when a tag is a certain value? Or does this...
2,710
Hi guys, This is my first thread in this forum. I'm wondering if some of you here are experts in using Wonderware System Platform 2014 R2. I'm...
3,260
Hi, I have a problem in Factory Talk SE. I have a numeric input variable which is supposed to be in millisecond (ms) and I have the tag in PLC in...
1,567