Change IP addresses from Runtime in Panelview
So I have a panelview plus 600 hooked to a L33er plc. Plc is 192.168.10.2 and the panelview is 192.168.10.3. I would like to be able to change the IP address of the plc from the runtime application (change both the ip address on the plc and also the plc ip address the HMI should be looking for) which will of course end up in a comms error but then also change the panelview Ip address through the runtime, hence restoring communications. Is there a way to do this?
|
![]() |
![]() |
#2 |
Lifetime Supporting Member + Moderator
|
Everything is possible with enough custom software, but there are no ordinary or easy methods to do what you describe, because there are straightforward development software tools that do each of those functions.
A ControlLogix can programmatically set its own IP address. The FactoryTalk Linx Shortcut configuration in a PanelView Plus cannot be changed programmatically by the FactoryTalk View application. The IP address of the PanelView Plus terminal itself is set using the operating system configuration tools via the Configuration Mode menus or the Windows CE/Windows 10 IoT Core desktop. |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Modbus/TCP Proxy for dynamic public IP addresses? | ryangriggs | LIVE PLC Questions And Answers | 1 | May 23rd, 2018 01:08 PM |
Panelview 7 Communicatios Ethernet IP | josecarias | LIVE PLC Questions And Answers | 1 | December 13th, 2017 12:12 PM |
PanelView Plus Password Change | ASF | LIVE PLC Questions And Answers | 5 | June 1st, 2016 08:01 PM |
Change IP ML1400 via G306 redlion | amfalcon1 | LIVE PLC Questions And Answers | 1 | October 15th, 2014 04:19 PM |
Need Panelview protocol change to Ethernet IP from DF1 | rguimond | LIVE PLC Questions And Answers | 1 | June 25th, 2010 06:53 PM |