Yaskawa Motionworks Program
I have a spin welding machine utilizing a Yaskawa Sigma II motor, with an MP940 controller. I am attempting to change the weld characteristics from a discrete "move" profile to a Constant torque move. I have had success with the weld but have stumbled in trying to recieve feedback (the whole point of the change). I tell the system to move with a constant torque until it reaches a target velocity, and then come to a controlled decel stop. So far, so good. I want to moniter the distance it traveled (each cycle) and compare that to target window for QC feedback to the PLC. That's the problem
I cannot find a System Parameter that contains that data and none can be reset (they're all Read Only). And for some reason, I cannot get the program let me set a user defined variable I named "home" to be equal to one of the System Variables at the start of the cycle. Then, at least I could do the math, and have my data. Thanks for any help. |
![]() |
![]() |
#2 |
Member
|
I have a feeling you are using MotionWorks Plus, not MotionWorks. They are quite different.
In MotionWorks, the feedback position can be read from input address ILC008 (32-bit value). You cannot reset this position directly, but you can either use motion command 9 (motion command register is OWC020) or place a value into home offset register OLC02A. Now, if you use MotionWorks Plus I cannot be of much help, sorry. Call Greg Findlay at Yaskawa office in Waukegan, 847-887-7000, he might be able either to help or give a name of someone who can.
__________________
Don't trust, don't fear, don't beg... |
![]() |
![]() |
#3 |
Member
![]() ![]() Join Date: Nov 2007
Location: Elgin, IL
Posts: 2
|
You are correct, It IS MotionWorks Plus. My mistake.
Thanks |
![]() |
![]() |
#4 |
Member
![]() ![]() Join Date: Feb 2023
Location: spain
Posts: 3
|
help mp940
hi, i need motionworks for programming a mp940 that erase program, please help me, i dont see software in all internet, i need mpe720 ver5 or motionworks+.
any have it? very very thanks. |
![]() |
![]() |
#5 |
Member
![]() ![]() Join Date: Jan 2012
Location: Ohio
Posts: 70
|
Contact Yaskawa Europe. It is still available.
|
![]() |
![]() |
#6 |
Member
![]() ![]() Join Date: Apr 2019
Location: spain
Posts: 11
|
Hi, last Friday yaskawa Europe (Germany) says that no have this software yet, and not say any solution, could you have it?
I'm desperate!! |
![]() |
![]() |
#7 |
Member
![]() ![]() Join Date: Jan 2012
Location: Ohio
Posts: 70
|
Yaskawa America sells it, but I don't think they can sell it outside of the US. I will do a little more research.
|
![]() |
![]() |
#8 |
Member
![]() ![]() Join Date: Jan 2012
Location: Ohio
Posts: 70
|
Yaskawa America or Europe doesn't sell this as a regular item. It can only be sold to customers that are known to have knowledge of how to use it. Can you contact the OEM, or maybe a Yaskawa integrator to help you?
Last edited by sparky66; February 8th, 2023 at 10:28 AM. |
![]() |
![]() |
#9 |
Member
![]() ![]() Join Date: Apr 2019
Location: spain
Posts: 11
|
Hi, yaskawa Europe sell me mp720, but i have a new problem i don't can connect to PC with mp940 and windows 10, any solution?
Thanks. |
![]() |
![]() |
#10 |
Member
![]() ![]() Join Date: Jan 2012
Location: Ohio
Posts: 70
|
Are you saying that MPE720 doesn't work with Windows 10? Are you using the YS15 cable?
|
![]() |
![]() |
#11 |
Member
![]() ![]() Join Date: Apr 2019
Location: spain
Posts: 11
|
Hi, yes, it works on windows 10, but i don't communicate to mp940 with a prolific USB converter, i test with ys13 and ys15, any solution please?
|
![]() |
![]() |
#12 |
Member
![]() ![]() Join Date: Apr 2019
Location: spain
Posts: 11
|
I create a group folder, order folder and PLC folder, and then when I click log on don't communicate to mp940.
|
![]() |
![]() |
#13 |
Member
![]() ![]() Join Date: Apr 2019
Location: spain
Posts: 11
|
Error:
CPDH_COM_012 Cannot go online. Check hardware and "Communication process" settings |
![]() |
![]() |
#14 |
Member
![]() ![]() Join Date: Jan 2012
Location: Ohio
Posts: 70
|
Should work with the YS15 in Port 1. Have you set the target to MP940?
|
![]() |
![]() |
#15 |
Member
![]() ![]() Join Date: Apr 2019
Location: spain
Posts: 11
|
How, yes i use port1 with USB prolific and ys15 to mp940, what could you say with target to mp940?
Thanks |
![]() |
![]() |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Download a PLC program? Transport memories? | Mc_Topaz | LIVE PLC Questions And Answers | 10 | April 25th, 2011 10:40 PM |
Cyclic program operation in s7-300 | mhmtfthnl | LIVE PLC Questions And Answers | 9 | October 30th, 2010 10:56 PM |
adding documentation to existing program | senen | LIVE PLC Questions And Answers | 20 | December 8th, 2004 10:18 PM |
PLC Program Management | zmanvortex | LIVE PLC Questions And Answers | 5 | November 1st, 2004 11:03 AM |
S7 CPU Parameterisation problems after loading program | RMA | LIVE PLC Questions And Answers | 12 | October 7th, 2004 10:12 AM |