3 pumps and 1 flowmeter
blima
Aug 2010
Lisbon
96
Hello!
I have a project with 3 water pumps, controlled by ABB ACS500 drives, and only 1 flowmeter at the exit of the pipeline, that is commom to all. Normally I will work only with one pump, but I can have the situation where I need two pumps.
So, I think that best solution is:
Desired flow = 50 m3/h
Pump 1: PID closed loop for 25m3/h with the return analog value from flowmeter
Pump 2: Fixed frequency for 25m3/h
Is this the best solution?
I have read thies thread:
http://www.plctalk.net/qanda/showthread.php?t=40590&page=2
And is quite nice but just want to confirm if I am one the right track.
Regards,
Bruno
Hi Blima,
First of all, do you have no-return-valves on all of your pumps?
If not, you might be "forced" to run them at the same frequency.
Also look at your pump curves. It might be beneficial to treat your pump as one unit, and just run them in parallel.
If you have flat curves for your speeds, and no-return-valves, you are spot on :).
IF these are centrifugal pumps and IF the discharge head is not absolutely constant then the flow rate vs. frequency relationship isn't constant. Furthermore, "identical" pumps never are, and discharge piping resistance isn't often identical.
I suggest you run the two pumps at approximately the same frequency. I also suggest that you monitor as a secondary parameter pump power draw from the VFD and trim the speed to maintain equal power - assuming the discharge pressure seen by each pump is nearly equal that will mean each pump is at nearly equal flow.
dear all.. i am designing the Sea Water Intake pump which the 4 pumps will be operated parallel, and 1 pump will be as stand by pump The pump data...
157
Hello Guys, I have tried the programming but can't twist my mind to make it work correctly. I'm using S71200 and TIA Portal. My system has...
200
I have been reading everything I can find on the P_LLS the last 2 days but I am still having trouble understanding how the P_LLS swaps beyond 2...
580
Hi, I started off my career in PLC programming doing water/wastewater on AB around 20 years ago, but then moved overseas a few years later and...
57
12,066
Good morning everybody, I hope you are very well. I share with you the information of the PLC LOGO! Siemens and expansions that we have...
1,088