I currently have a E1101 talking across Modbus to a DSE 5220 Genset Controller using the following driver…
Com1 – modicon Master/Modbus Naster 4.04.01
I am able to read from the controller as the Driver uses the Modbus Multiple Read Command (03), but to write commands the controller required a Modbus Write Multiple Registers Command (16)
Ie… Multiple Command (Slave 10) should be “0A 16 ………”
At the moment when writing the E1000 Modicon driver is sending “0A 06 10 00 00 08 8D B7”
Is there any way I can get the driver to send a multiple write command ???