When using 4 to 20mA I have been using 3277 to 16384 for the input min and max.
We had new controls put in for a machine several years ago and for the actual drive current amp SCP they are using;
input min 3277.0
input max 16383.0 SHOULD THIS BE 16384.0?
scaled min 0.0
scaled max 50.0
Ever since the install several years ago there have nuisance alarms for high amps.
On the VFD for amps it is pulling 6.7 amps but the panelview plus is showing 8.0 and up. Could the last digit difference on the input max be causing this error?
Thank you