Can an RX3i CPU communicate via Modbus TCP and EGD on one ethernet port?
defcon.klaxon
Feb 2015
Far NorCal
616
After reading through some older threads and checking out my old friend GFK-2224, it sounds like an RX3i CPU can talk Modbus TCP, this much I'm fairly confident about. But what I wonder is, if my CPU (CPE305) has just a single ethernet port, can the single ethernet port communicate multiple languages simultaneously? For example, my PLC to PLC comms are EGD. Could the CPU also, on top of EGD, communicate with a Modbus TCP device on the same network? I'm thinking no, you'd need an ETM001 module; can someone confirm or disconfirm this?
Yes it should so long as you do not exceed the total number of available channels.
From GFK-2934A
Embedded Ethernet interface supports up to 32 simultaneous SRTP Server connections, up to 16 simultaneous Modbus/TCP Server connections, and up to 16simultaneous communications channels of either SRTP Channels or Modbus/TCP Client channels. For details, refer to the PACSystems RX7i & RX3i TCP/IP Ethernet Communications User Manual, GFK-2224.
I would upgrade the CPU to the latest firmware which is 9.40.
I had a processor go out on a PLC rack. I am trying to use a different processor because that is what the customer had available. Original was...
1,252
Hey guys, I'm on site integrating for the first day on a project where I'm programming RX3i (CPU 305) controllers and have hit a snag. At the...
2,423
How long do these Energy Packs last?? I seem to be loosing them in about 2 years. Are they be hot swapped? I would assume so...wouldn't you...
2,084
I have a system using Rx3I CRU320 redundant CPU with Proficy Machine Edition Software. In the hardware configuration of each CPU module, under...
422
Hi, we are using Rx3i CRU320 redundant PLC system and we noticed a discrepancy between Primary and Secondary controller. Couple of variables (DI)...
313