Hi!

Hopefully I'm allowed to ask this question here, if not the admin is free to delete it.

We have a standard cabinet we ship to our customers. Now there is a customer that want's to have SSR relays instead of regular mechanical relays. We tried talking him out of it with no succes. So now I've tried gather information how to use SSRs. I know it's basicly same functions as a mechanical relay and here iare my concerns.


It seems they are very sensitive on the input side, how sensitive is that? I will try to wire to seperate the main AC and the control circuit DC as mush as possible.

The SSR relay only has 1 "pole". I have relays that have 4 poles, my best guess here is that I use 4 SSRs in parallell?

I have mechanical contacts i series and in parallell, with SSR is it possible to connect them in series or parallell? I think you can but better safe then sorry.

I have attached a file with little schematics and text.

Thanks /Tim
Attached Images
File Type: jpg SSR.jpg (27.9 KB, 234 views)
  Reply With Quote
Old October 28th, 2015, 03:25 AM   #2
kallileo
Lifetime Supporting Member
Greece

kallileo is offline
 
Join Date: Jun 2008
Location: Thessaloniki, Macedonia, Hellas
Posts: 323
This could be useful:

Using Solid State Relays in parallel and/or series
  Reply With Quote
Old October 28th, 2015, 05:11 AM   #3
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,576
Are there any contactors in the panel? If so and your customer is happy with contactors then just replace the relays with contactor/relays:

http://www.eaton.eu/Europe/Electrica...DILA/index.htm
  Reply With Quote
Old October 28th, 2015, 05:39 AM   #4
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,493
My first impression, is that your customer is a complete idiot.
Why does your customer want this?

SSR's are great as replacements for mercury relays for heaters, yes. Or other power switching duty.

For controls, they are completely stupid.
Poor isolation, high insertion loss, problems with analog or mixed voltage signals...
/shrug.
__________________
------------------------------------
How to ask questions the SMART Way!

Look First, Ask Second!

  Reply With Quote
Old October 28th, 2015, 07:59 AM   #5
RoTaTech
Member
Canada

RoTaTech is offline
 
RoTaTech's Avatar
 
Join Date: May 2003
Location: Cobourg, ON, Canada
Posts: 397
If he *wants SSRs, there are some electronic factors to consider. In your diagram of the contacts in parallel, SSR should be fine because they have a load (the coil). But if one were wiring four SSR contacts in parallel to a high-impedance input (for example, a PLC input), there could be enough leakage current to trigger an input. SSRs should have a load with enough impedance to pull down leakage.

Better safe THAN sorry - you don't really want to be both safe and then sorry . . .
__________________
"Nice mirror!" said Tom reflectively.
  Reply With Quote
Old October 28th, 2015, 10:06 AM   #6
Phil Buchanan
Lifetime Supporting Member
United States

Phil Buchanan is offline
 
Phil Buchanan's Avatar
 
Join Date: Jun 2015
Location: Atlanta, Georgia
Posts: 541
I can understand the end user asking for SSR's where possible as it will give him a more reliable control system with a higher MTBF if done correctly.

I use the units in the link below a lot for control as you can get them with built in leakage protection and the handle a fair load size.

http://www.ab.com/en/epub/catalogs/1...roduction.html

SSR's are no issue on digital signals if you use control rated SSR's and they are sized correctly for the impedance of the circuit and devices being controlled. The problem comes in when people think they can just throw an SSR where a mechanical relay was with not though and it will be all smiles and that's just not the case most often.

With that said though I try to avoid relays if at all possible. Some people in the industry get carried away with isolation and interfacing. i have seen panels that have a relay on every input when the input was a prox or limit switch which could have been directly connected.

Systems like this are more complex and harder for the average maintenance tech to troubleshoot and repair and have a lower MTBF.

PLC's were designed to simplify control systems and replace a lot of relay logic and some add a plc and ton's of relays where they are not need and it makes no sense.

I have ran across a lot of systems with a plc and so many interface relays that i could have used relay logic alone with not plc and had a much more simple and reliable circuit.

Not saying that's the situation the OP has but just something to keep in mind.

Last edited by Phil Buchanan; October 28th, 2015 at 10:08 AM.
  Reply With Quote
Old October 28th, 2015, 10:11 AM   #7
Phil Buchanan
Lifetime Supporting Member
United States

Phil Buchanan is offline
 
Phil Buchanan's Avatar
 
Join Date: Jun 2015
Location: Atlanta, Georgia
Posts: 541
Here is another piece of literature that may be helpful to you. Beware it's a real page turner.

http://literature.rockwellautomation...t001_-en-e.pdf
  Reply With Quote
Old October 28th, 2015, 10:38 AM   #8
keithkyll
Member
United States

keithkyll is offline
 
Join Date: Jul 2005
Location: Heath, TX
Posts: 2,033
The system is relay logic. I'm thinking the customer is asking for Solid State, not SSR.
Replace the entire system with a PLC.
  Reply With Quote
Old October 28th, 2015, 12:53 PM   #9
rQx
Lifetime Supporting Member
Sweden

rQx is offline
 
Join Date: Oct 2010
Location: Trelleborg
Posts: 904
They have only stated that the relays must be SSR but not the contactors. Which is wierd because they said they didn't want any mechanical switches, we must switch our level sensors to non mechanical and pressure sensors to analog etc etc.

Maybe we can use contactor relays instead, I'll have to ask the customer about that. Problem is that I haven't got direct contact with the end customer.

Our SSRs contacts will go to a PLC aswell, but then I can find SSRs designed to not leak current?

PBuchanan, I have read that and that's where all my questions come from

The system contains both some relays and a LOGO usually. But this customer doesen't want the LOGO aswell. So I have to run every input and output to terminals to their DCS. Making our cabinet a slave cabinet with only some manual functions.

This customer is like.... give me a break.
  Reply With Quote
Old October 28th, 2015, 01:22 PM   #10
just the cowboy
Member
United States

just the cowboy is offline
 
just the cowboy's Avatar
 
Join Date: Nov 2013
Location: Pa
Posts: 264
Hard to find NC contacts

Also try searching for the SSR you will have a hard to find NC contacts.

Solid state for power contacts are fine but if they want control just go PLC.
__________________
Work safe, have fun, don't die
  Reply With Quote
Old October 28th, 2015, 01:47 PM   #11
rQx
Lifetime Supporting Member
Sweden

rQx is offline
 
Join Date: Oct 2010
Location: Trelleborg
Posts: 904
Quote:
Originally Posted by just the cowboy View Post
Also try searching for the SSR you will have a hard to find NC contacts.

Solid state for power contacts are fine but if they want control just go PLC.
Yes I know NC is hard to find but I think that maybe I can redesign so I only have NO.

Problem is customer is specifik about they don't want PLC.
  Reply With Quote
Old October 28th, 2015, 02:02 PM   #12
MHennel
Member
United States

MHennel is offline
 
Join Date: Jun 2002
Location: Cincinnati, OH
Posts: 53
I have used Crydom relays for many years with no problems

http://www.crydom.com/en/. They have a wide selection SSR of both AC and DC.
  Reply With Quote
Old October 28th, 2015, 07:33 PM   #13
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 2,039
You are going to need to know if that control circuit is AC or DC, it makes a big difference on the type of SSRs you use. The drawing you clipped doesn't show that.
  Reply With Quote
Old October 29th, 2015, 02:12 AM   #14
rQx
Lifetime Supporting Member
Sweden

rQx is offline
 
Join Date: Oct 2010
Location: Trelleborg
Posts: 904
It is 24VDC, I decide what control circuit we are using since I am designing the cabinet
  Reply With Quote
Old October 29th, 2015, 01:36 PM   #15
rQx
Lifetime Supporting Member
Sweden

rQx is offline
 
Join Date: Oct 2010
Location: Trelleborg
Posts: 904
Ok, so if I got this straight.

The SSR have a leakage current when they are off and a voltage drop when they are on.

Am I right in assuming that if I want to have two SSR contacts in series, I want a low voltage drop so that I have enough voltage left for my load?

And it's always better to have a SSR with low leakage current? So that I don't trigger more sensitive inputs on a PLC for example? In other words it's not bad to have a low leakage current even if I don't need it to be?

I have found a relay from Crydom: http://www.crydom.com/en/products/catalog/e_d_dc.pdf

Load: 5A
Voltage drop: 0.3V
Leakage current: 20uA

I think this would suit me pretty good in all my areas.
For the most part my relays will go to indication lights (Allen Bradley 800F series LED), for controlling 24VDC contactors (with low consumptions coils and diode) and to a LOGO module from siemens.

Am I on the right track here?
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Optocouplers & Solid state Relays Questor22 LIVE PLC Questions And Answers 7 March 20th, 2014 07:49 AM
Solid State Relays Jon R LIVE PLC Questions And Answers 3 July 13th, 2008 12:15 PM
Solid State problems Heino Geerdens LIVE PLC Questions And Answers 6 May 9th, 2006 10:59 AM
Solid State Relays DL06 LIVE PLC Questions And Answers 10 March 24th, 2006 07:48 AM
Solid State Relays GUEST LIVE PLC Questions And Answers 7 October 20th, 2004 05:05 PM


All times are GMT -4. The time now is 10:48 AM.


.