FactotyTalk View ME acknowledge alarm

pr_wainwright

Member
Join Date
Jun 2011
Location
Stockton on Tees
Posts
109
Hi,
I have a client who wishes to be able to acknowledge individual alarms on a PanelView Plus 6 HMI. E.g. an alarm comes in & the associated graphic flashes red. Once the alarm is acknowledged the graphic stops flashing but remains red. Is there some way i can detect if an individual alarm has been acknowledged in my animation script? E.g. mytag.ack / mytag.unack?

Thanks
Paul.
 
Hi Paul

I know you can show ack and unack works in the alarm history and you can assign a color to each but I am not are about getting the back round color to flash. If you look in the alarm history and then look at display I think there you selected what you woils like to display.
You could create your own alarm display of you really wanted to but it would be a lot of work .

Donnchadh
 
go to Alarm setup and look under the advanced tab you will Tags for use there. Assign your tag to the ones you want to use and write code in plc to to determine the difference. Once you get to the advance tab use the help button to get info on tags. Quickest way to the location in the help files.

You can also set individual tags for alarms on the trigger page by selecting the trigger and filling out tag info. Again click help for definition from that page.
 
Last edited:

Similar Topics

I have two identical machines running similar HMI projects, the only difference is one is done in FactoryTalk View Version 10 and the other is...
Replies
0
Views
25
I am using Factory Talk view Machine Edition Runtime HMI. I want to configure on button in such way that when i press this button I want to...
Replies
1
Views
52
Hello, I'm using FactoryTalk View ME V10. I created a valve as a global object with multiple parameters and when the object is being used at the...
Replies
2
Views
129
Hello all, I was modifying an HMI in factory talk and went to change a go to display button using the ... to select from a list as I had done...
Replies
4
Views
172
Hello, We recently upgraded our control server to a newer model. After the transition we are experiencing issues with our trend graphs to where...
Replies
2
Views
120
Back
Top Bottom