bryonc1213
Member
Trying to control some outputs using AB SLC 150 1745-LP151, 1745-E103, and 1745-E105
Trying to control outputs using an RTF timer as I want the output for duration from 3-15 seconds for each of about 12 outputs
201 start button NO, 004 NO Is actually NC with output 14 off (relay4 when on 3 will be on) latch to NO 901 timer pre 0000
901 NO, Output RTF 902 pre 120 seconds
902 NO, Output RTF 903 pre 003
903 NO, Output 112 (coal loader dumps for 3 seconds then off
902 NO, 901 NC, Output 901 reset 0000
Basically what I have been trying to do is start a 2 minute timer 902 during the 2 minutes complete a series of timed duration output turning on an output for say 3 seconds to 15 seconds at the end of 2 minutes the 903 (in this example) is done and resets the timers and allows a repeat operation at the press of 201 after 2 minutes has expired
Control is based on relay (11, 12 MCR) , one of the reset relay controlled by relay output 14 NC off input 004 is on and with 14 output true Input 3 is on and 4 is Off, 201 is the start and output are 211-216 and, 210 is an always hot status input and outputs 11 and 12 are MCR Power on There are are about 12 durations to control this is only of them I do have a complete matrix of the layout but this basically would repeat every 3 rungs or so using PCIS to operate via a computer link any help or ideas is appreciated
Trying to control outputs using an RTF timer as I want the output for duration from 3-15 seconds for each of about 12 outputs
201 start button NO, 004 NO Is actually NC with output 14 off (relay4 when on 3 will be on) latch to NO 901 timer pre 0000
901 NO, Output RTF 902 pre 120 seconds
902 NO, Output RTF 903 pre 003
903 NO, Output 112 (coal loader dumps for 3 seconds then off
902 NO, 901 NC, Output 901 reset 0000
Basically what I have been trying to do is start a 2 minute timer 902 during the 2 minutes complete a series of timed duration output turning on an output for say 3 seconds to 15 seconds at the end of 2 minutes the 903 (in this example) is done and resets the timers and allows a repeat operation at the press of 201 after 2 minutes has expired
Control is based on relay (11, 12 MCR) , one of the reset relay controlled by relay output 14 NC off input 004 is on and with 14 output true Input 3 is on and 4 is Off, 201 is the start and output are 211-216 and, 210 is an always hot status input and outputs 11 and 12 are MCR Power on There are are about 12 durations to control this is only of them I do have a complete matrix of the layout but this basically would repeat every 3 rungs or so using PCIS to operate via a computer link any help or ideas is appreciated