so Machine basic MSG3 function block
lesmar96
May 2017
PA
520
in SoMachine Basic v 1.5 What is use of the MSG3 function block? Is it simply to monitor the status of the ethernet communication? Is the MSG3.E bit report an error in the comm? The problem I am working with a program that uses this bit to report an error, but it does not turn on even when I have the ethernet cables disconnected between the two plcs communicating over Modbus TCP/IP.
Please adsvise on the proper use of this functio block. Thanks!
I think msg3 is just a name that was given to the block. Can you tell us the object type of the block
msg3 block is old messaging block for ethernet
yes, this is a messaging block for ethernet, but what does is do? Ethernet comm will work without it. Is it simply to monitor? Seems to refresh the communication every time the NO contact ahead of it becomes true.
I first learned about this block in one of the templates on somachine v.1. titled xSample_ModubsTCP_Wireless Push Button ReadStatus. This sample program uses this MSG3 block.
Any more advice would be helpful.
does any one have more suggestions?
Maybe this is a function rarely used or a better way to do it?
If you have only HMI or Scada connected to PLC you don't need msg block at all 99% of time.
MSG blocks are used for communication to other PLCs or field devices. MSG block is used on older twido controllers. M221 have different methods and blocks for communications but also MSG block is possible to use.
It is used communicate and check status of communication after querys are sended.
msg1 = port1, msg2 = port2 and msg3 = ethernet (port3)
http://www2.schneider-electric.com/... Modbus Communication_Quick Guide_File3.PDF
My program is communication between to plcs. This is actually a program I did not build so I was trying to figure out the details of it. Looks like %SW65 could be used to monitor the ethernet status.
Hello All, I am stumped on how to convert a %MW to a %MF using Machine Expert Basic and a Modicon M221. The help files show a word to a double...
153
Hey Programmers, Heres todays puzzle I was trying to solve... I have a Modbus TCP network with two Modicon M221 controllers live on my work bench...
487
In the last two months I have had an issue after making some online changes between the software and an Schneider M221 PLC via ethernet network...
1,113
Hi all, I've been trying to develop modbus rtu program between uv balasts and plc ı'have 6 slave balast.I am reading fault run voltages etc...
1,224
Hello Everyone, Is there a procedure in the Schneider EcoStructure Machne Basic program to save the controllers runtime memory word data (ie...
2,383