A/B Analog Current Transmitter wiring dilemma

Hello all,

I'm trying the wire up a Baumer Inductive Conductivity/Temp combination sensor to a 1769 combo analog in/out module.

The sensor is a new install; according the the manual print the transmitter uses the two 4 pin m13.
One side is for power and conductivity. Wiring as follows:

Brown: Supply+
White: Conductivity -
Blue: Supply -
Black: Conductivity +

the other connector (temp) is

White: Temp -
Black: Temp +

The other two wires on the cable/plug are for external input we're not using.


My connections on the analog card are V in + (1)
V in - (1)
I in + (1)


The way I have it currently wired I can monitor the input and it's fluctuating around -30,000. The sensor is already configured (the 4 and the 20) so by rights it should be reading 0 (the scaling is 0-32767 input min to max).

Thoughts on wiring this?
  Reply With Quote
Old January 17th, 2020, 10:19 AM   #2
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,438
Looks like you will need to use 2) 4-20mA inputs. One for conductivity and the other for temp. The thing you need to find out is if the device supply’s the 4-20mA signal (Active) or if you need to supply the power from your panel (Passive). Once you know that we can help with the wiring.
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old January 17th, 2020, 10:32 AM   #3
toddp65
Member
United States

toddp65 is offline
 
Join Date: Aug 2014
Location: Florence, Ky
Posts: 227
Quote:
Originally Posted by Bullzi View Post
Looks like you will need to use 2) 4-20mA inputs. One for conductivity and the other for temp. The thing you need to find out is if the device supply’s the 4-20mA signal (Active) or if you need to supply the power from your panel (Passive). Once you know that we can help with the wiring.
Thanks--yes, it has two separate cables. The conductivity side also provides the 24 vdc and it has cond + and - and uses all four wires.. The temp cable only uses two pins.I'm using inputs 1 and 3 on the card, they're already enable and configured on the module config.

Last edited by toddp65; January 17th, 2020 at 10:36 AM.
  Reply With Quote
Old January 17th, 2020, 10:37 AM   #4
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 10,454
Based on your data being negative, I suspect the polarity of the data wiring is backerdz.

We're still not clear on whether the signals are active or passive. Use a multimeter or loop calibrator to find out. With power applied to the device, test each pair with a meter (while unhooked from your PLC/panel wiring). If you get a mA reading with a multimeter or with a loop calibrator, then the device supplies the voltage for the signals. If you don't then you will need to apply 24vdc to the "+" wire, and you will get the mA data back on the "-" wire.

Note that some loop calibrators have a loop power mode. Don't use that mode at first, but if you get nothing, you can try loop power mode to prove that the signal works and that you need to wire it to a power supply (separately from the device power).
__________________
You can choose a ready guide in some celestial voice. If you choose not to decide you still have made a choice.

Last edited by OkiePC; January 17th, 2020 at 10:43 AM.
  Reply With Quote
Old January 17th, 2020, 10:49 AM   #5
toddp65
Member
United States

toddp65 is offline
 
Join Date: Aug 2014
Location: Florence, Ky
Posts: 227
The black and white wires coming from transmitter conductivity side is reading 4 mA (that's what the display says it's transmitting as well, the line is empty) according to my analog meter. The temp is 5.6 (seems off).

So far it seems like a module wiring issue

when i swapped the wires, it went straight to -32767 and didn't move. In the other config it's -30,000 and fluctuating (still wrong)

Last edited by toddp65; January 17th, 2020 at 10:51 AM.
  Reply With Quote
Old January 17th, 2020, 11:04 AM   #6
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,545
Quote:
Originally Posted by toddp65 View Post
Wiring as follows:

Brown: Supply+
White: Conductivity -
Blue: Supply -
Black: Conductivity +

the other connector (temp) is

White: Temp -
Black: Temp +

That certainly looks like a typical 4 wire transmitter, which wouldn't require a separate power supply for loop excitation. I suspect that the single power supply connection provides the loop excitation power for the temperature output as well as the conductivity output.

I'd need to know the exact part number and configuration of the IO module to specify the correct wiring, but if it's a 1769-IF4FXOF2F, then your output positive should probably connect to both the V in x+ and I in x+ terminals while the output negative would connect to the ANLG Com terminal.
__________________
  Reply With Quote
Old January 17th, 2020, 11:19 AM   #7
toddp65
Member
United States

toddp65 is offline
 
Join Date: Aug 2014
Location: Florence, Ky
Posts: 227
Quote:
Originally Posted by Bit_Bucket_07 View Post
That certainly looks like a typical 4 wire transmitter, which wouldn't require a separate power supply for loop excitation. I suspect that the single power supply connection provides the loop excitation power for the temperature output as well as the conductivity output.

I'd need to know the exact part number and configuration of the IO module to specify the correct wiring, but if it's a 1769-IF4FXOF2F, then your output positive should probably connect to both the V in x+ and I in x+ terminals while the output negative would connect to the ANLG Com terminal.
that's the correct module number
  Reply With Quote
Old January 17th, 2020, 11:40 AM   #8
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,545
Quote:
Originally Posted by toddp65 View Post
that's the correct module number


Then see Page 14 in the linked document for the wiring diagram.
__________________
  Reply With Quote
Old January 17th, 2020, 11:45 AM   #9
toddp65
Member
United States

toddp65 is offline
 
Join Date: Aug 2014
Location: Florence, Ky
Posts: 227
I'll check the wiring; I know it's not like this but I've had it configured multiple ways.

Is it the diff or two wire current transmitter?
  Reply With Quote
Old January 17th, 2020, 04:59 PM   #10
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,545
Quote:
Originally Posted by toddp65 View Post
I'll check the wiring; I know it's not like this but I've had it configured multiple ways.

Is it the diff or two wire current transmitter?

It's not a two wire transmitter.
__________________
  Reply With Quote
Old January 17th, 2020, 05:04 PM   #11
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,438
I would wire it up like they show the Differential Current Transmitter. Don't forget the jumpers they show in the diagram.
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Old January 19th, 2020, 09:45 AM   #12
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,545
So, does it work now?
__________________
  Reply With Quote
Old January 20th, 2020, 09:17 AM   #13
toddp65
Member
United States

toddp65 is offline
 
Join Date: Aug 2014
Location: Florence, Ky
Posts: 227
Yes..perhaps. But the scaling isn't true to the actual data. I've been trying to manipulate it to fit (ex: with 0-60 conductivity I've had to lower the max to bring my actual temp to what it is but when I go to what should be 0 it isn't accurate. Still playing with it. Odd thing is they value there whether the jumpers are installed or not.


Side note: I have these value ported over to the panelview plus--the tag is identical and it's worded the same way every other original numeric display is, yet I don't see it on my PVP after downloading it. Thoughts on this as well?

Last edited by toddp65; January 20th, 2020 at 09:24 AM.
  Reply With Quote
Old January 20th, 2020, 10:41 AM   #14
toddp65
Member
United States

toddp65 is offline
 
Join Date: Aug 2014
Location: Florence, Ky
Posts: 227
Figured out the PVP issue but the analog inputs are still incorrect. I have variables to work with but they're difficult to scale; the transmitter says it's sending out 4 mA but my engineering units coming in isn't the equivalent of 4 mA (3200) in my SCL block analog input (or in the controller tags tree ) it's like 3700.
  Reply With Quote
Old January 20th, 2020, 04:47 PM   #15
Bullzi
Lifetime Supporting Member
United States

Bullzi is offline
 
Join Date: Jun 2012
Location: Colorado
Posts: 1,438
Few more questions:

1. How do you have the Input set up? Raw/Proportional or Engineering Units? See the Attached snip.
2. Can you measure the actual current coming out of the instrument? It could be saying that it is sending 4mA but may be sending more due to calibration.
3. Any chance that you could be getting noise on the line? Do you have your shields grounded on one end only?
Attached Images
File Type: png Analog Set up snip.png (19.2 KB, 38 views)
__________________
There is never enough money to do it right but there is always enough money to do it again.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Analog Output current range. mocca-fixer LIVE PLC Questions And Answers 0 August 25th, 2016 03:27 PM
how to take the data from level transmitter to analog input omron? kartika LIVE PLC Questions And Answers 3 July 29th, 2011 06:28 AM
how to take the data from level transmitter to analog input omronCS1W-AD16? kartika LIVE PLC Questions And Answers 0 July 29th, 2011 03:38 AM
Transmitter wiring GregPLC LIVE PLC Questions And Answers 3 January 29th, 2003 10:13 PM
AB Analog Input Module Wiring... Eric Nelson LIVE PLC Questions And Answers 3 May 6th, 2002 08:37 AM


All times are GMT -5. The time now is 11:07 AM.


.