Pointer Triac versus Relay output card

Just wanted to know what are people's thought on a triac output versus relay output cards? I'm working with the Allen Bradley SLC line, 1747-OA16 and 1747-OW16 output cards. I've used the OA16 before to control a solenoid manifold which operates high pressure valves. I snub each coil of course, for arc-quenching. I need to build another PLC controlled solenoid rack and it has worked in the past (still works today after years of service) using a 120V TRIAC output card, but it doesn't mean it is right, or the best way to do it.

I'm just wondering when it is better to use a triac or relay output card. What are the pros and cons? Does load current determine one or the other?
  Reply With Quote
Old February 25th, 2015, 11:23 PM   #2
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 11,507
Relays have a finite life. Triacs, and other solid state outputs, have infinite life when done right as you seem to have experienced.

Relays generally handle more load.

Triacs "leak". Triacs, and most other solid state outputs leak enough current to fool a high impedance voltmeter in an open circuit condition when in the off state. Also, the off state leakage may cause very low power field devices to get "stuck" on. Other symptoms may include flickering, humming, or lamps that glow dimly.

Relays are "dry contacts" so they allow isolation from otherwise independent voltages and circuits. When they are off, they are all the way off. They don't "leak".

That is the "nutshell" version in random order.
__________________
You've been taken, but you don't know it yet.

Last edited by OkiePC; February 25th, 2015 at 11:29 PM.
  Reply With Quote
Old February 26th, 2015, 08:19 PM   #3
CeeDee
Member
United States

CeeDee is offline
 
Join Date: Jun 2014
Location: Bremerton, WA.
Posts: 94
That's a pretty good "nutshell" explanation. I like it. Thanks!
  Reply With Quote
Old February 26th, 2015, 08:22 PM   #4
ASF
Lifetime Supporting Member
Australia

ASF is offline
 
Join Date: Jun 2012
Location: Australia
Posts: 3,723
Every panel I build uses solid state outputs. The only two things I drive with them are slimline interface relays, or 22mm indicators on the panel door. I never drive field items or contactors straight from the outputs.

This way I get the more or less "infinite" life from my outputs that OkiePC suggests above, and then the relays, well, it's a whole lot cheaper and easier to replace a relay now and again than an output card.
  Reply With Quote
Old February 26th, 2015, 09:23 PM   #5
CeeDee
Member
United States

CeeDee is offline
 
Join Date: Jun 2014
Location: Bremerton, WA.
Posts: 94
Quote:
The only two things I drive with them are slimline interface relays, or 22mm indicators on the panel door.
I kind of like the idea of slimline relays. I just looked them up. Altech Corp were the first kind that popped up doing a G-search. Omega makes the same kind too. I've never used them before. I've had success with just using the -OA16 output card, each output fused, directly wired to the solenoid I needed to actuate. They are pretty small solenoids; probably the size of a standard SPDT automotive relay. I was always hesitant of using more relays to a setup that already works, adding more components that can fail and taking up a lot more real estate. Even with adding small ice-cube style relays the amount of room that 7 or 8 solenoid bank control would be significant. But you've definitely got me thinking... do these slimline relays have any plug in arch-suppressors you can add to them? Or, are they even necessary? The solid state output from the card is still essentially powering a coil within the slimline relay (even if it is a very tiny coil) and still susceptible to voltage spikes, right?

I attached a pdf file of the valves I control to get an idea with what I'm talking about.

It just doesn't say the current draw or inrush of the coil. I may have to do some in-use current tests. hmmm...
Attached Files
File Type: pdf Alpha-EN.PDF (215.5 KB, 14 views)

Last edited by CeeDee; February 26th, 2015 at 09:36 PM.
  Reply With Quote
Old February 27th, 2015, 12:15 AM   #6
rdrast
Lifetime Supporting Member
United States

rdrast is offline
 
rdrast's Avatar
 
Join Date: Apr 2003
Location: South Carolina Lowcountry
Posts: 5,537
All solid state outputs here, mostly 24VDC, but still a few legacy 120VAC ones, and unless the load exceeds the output capacity, we drive field devices directly.
In 10 years, I can count the actual number of failed outputs on one hand, with fingers left over. In fact, every one was on an older system, and was an SLC-500 AC output driving an oversized contactor.

I do go ahead and use these nice isolation relays but only if I am driving a load the output can't handle, need voltage translation (newer designs stick with all 24VDC outputs, no 120 on the PLC rack), or need actual isolation (contact closure to energize a drive for example).
__________________

  Reply With Quote
Old February 27th, 2015, 03:29 AM   #7
shooter
Member
Netherlands

shooter is offline
 
shooter's Avatar
 
Join Date: Sep 2002
Location: duketown
Posts: 2,711
DC does not leak, however AC does, so if loads are small <20 mA you will need a isolationrelay.
On DC a simple diode is good as snubber, in AC a resistor and capacitor or a VOR is needed, these overvoltage protection has or a limited life or makes leakage current.
__________________
shooter@home.nl
skype shooter paul.deelen
Computer Shooter
Paul Deelen
J. Wassenaerstraat 29
NL 5224 GG 's-Hertogenbosch
+31653300739
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Interposing relays Malador LIVE PLC Questions And Answers 23 March 2nd, 2013 01:52 AM
1734-OB8E Output Card Issue Denofar LIVE PLC Questions And Answers 0 March 19th, 2012 07:39 PM
AB Triac Output Card PatrickSlaughter LIVE PLC Questions And Answers 5 April 26th, 2010 12:58 PM
Triac Output Card plcengineer LIVE PLC Questions And Answers 2 April 3rd, 2008 10:31 PM
Sequential Logic to AB PLC Tze LIVE PLC Questions And Answers 7 January 4th, 2003 12:41 PM


All times are GMT -4. The time now is 05:31 AM.


.