Do I need a shielded wire for 4-20mA signal?

Cryogen

Member
Join Date
Oct 2005
Location
NH
Posts
151
I have a SLC 500 PLC with NI4 analog input card. I am using two 4-20mA signal coming from an RTD transmitter. The overall length of the cable is around 20ft. I have very limited knowledge in grounding and shielding. In my understanding, voltage signals are more susceptable to interference than current signals. So I am not sure if we need a shielded cable for this signal..

Please let me know what I should do.. Any documentation on basics of grounding/shielding would be helpful too..

Thanks for your time!
 
I would use shielded cable. Even if you don't have interference from any other source NOW, you might in the future from a new/changed process requiring components that would interfere with non-shielded wire.
 
Download this document from mrplc.com: EMC Guide

Help with selecting shielded cables:
Chapter 2 - Cables

Advice on termination of shielding:
Chapter 2 - Wiring Rules
 
Thanks for your replies.. It would definitely help me..

krk, I created a login on that site but still it doesn't let me download anything.. says

You Do Not Have Permission To Download Files In This Category

What should I do to see the files?
Thanks..
 

Similar Topics

I've got this 3-phase 575V motor that we're controlling with a VFD (Variable Frequency Drive), which has been quite the learning curve in itself...
Replies
10
Views
117
I'm fairly new to Rockwell software, I've had some basic training in the past but nothing too advanced. My company and I use Reliable products for...
Replies
11
Views
340
Hi all, I am having issues accessing my Cimplicity software - the site code changed after re-install and I am no longer able to attain a new key...
Replies
10
Views
167
Good day all! Can someone help me with the procedure to update Beijers E700 firmware? The Panel I am working on is firmware 2.04v and I would...
Replies
1
Views
70
Good evening. I display the step number of a SFC on a display. Sometimes, on a trip, it goes quickly through many steps and I need to prove to...
Replies
1
Views
130
Back
Top Bottom