ControlLogix: 120V AC Output putting out 87V ?

Is this the card, or what's driving the card? It's just a permissive being sent from one building to another.
  Reply With Quote
Old April 19th, 2017, 08:56 AM   #2
briancr
Member
South Africa

briancr is offline
 
Join Date: Jul 2007
Location: Port Elizabeth
Posts: 231
A bit more info will help a lot with suggestions

PLC? Module?

But gut feeling is a loose / bad neutral (or whatever its called on your side of the pond )


Brian
  Reply With Quote
Old April 19th, 2017, 09:02 AM   #3
cwal61
Member
United States

cwal61 is offline
 
Join Date: Jan 2011
Location: NC
Posts: 806
1. Is the output on or off when reading 87V?
2. Are you using a digital meter?
3. You most likely are using a solid state card instead of a relay card.

If off and using digital meter and a solid state card it's phantom voltage being read by the digital meter. They measure the potential between the leads. That's what you'll see with no load. If you had a old Simpson 180 meter (analog type) it would put enough resistance on the output to draw it down to 0V. When the output is off.
  Reply With Quote
Old April 19th, 2017, 09:12 AM   #4
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 429
[It's just a permissive being sent from one building to another. ]
That about says it all. Ground is not always ground. different potential between the 2 buildings.
This just shows why proper grounding (Bonding) in electrical systems is important.
Run a grounding conductor between the 2 buildings
  Reply With Quote
Old April 19th, 2017, 09:16 AM   #5
dmargineau
Lifetime Supporting Member
United States

dmargineau is offline
 
dmargineau's Avatar
 
Join Date: Dec 2011
Location: Midwest
Posts: 2,153
Quote:
Originally Posted by SoftwareJanitor View Post
Is this the card, or what's driving the card? It's just a permissive being sent from one building to another.
What is the output module Catalog Number?

Is it a TRIAC type?

You have to remember that a TRIAC is a current switch; a load connected to a TRIAC in the OFF state (even if it measures 87 VAC across) is not 'energized" since the current path is open.
  Reply With Quote
Old April 19th, 2017, 09:17 AM   #6
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,271
I'm betting (more than pocket change - but less than the rent) that he's dealing with a TRIAC module - and "leakage current" ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.

  Reply With Quote
Old April 19th, 2017, 10:11 AM   #7
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,103
Quote:
Originally Posted by Ron Beaufort View Post
I'm betting (more than pocket change - but less than the rent) that he's dealing with a TRIAC module - and "leakage current" ...
Yep. I've seen leakage current surprise quite a few folks over the years. Triac outputs are the worst, but surge suppression circuits can present leakage current even in a relay output.
__________________
  Reply With Quote
Old April 19th, 2017, 10:13 AM   #8
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,103
Quote:
Originally Posted by GaryS View Post
[It's just a permissive being sent from one building to another. ]
That about says it all. Ground is not always ground. different potential between the 2 buildings.
This just shows why proper grounding (Bonding) in electrical systems is important.
Run a grounding conductor between the 2 buildings
Ground continuity is crucially important, but it may also be necessary to add a resistor in parallel to the input in order to load the output circuit.

Either that, or employ an interposing relay.
__________________
  Reply With Quote
Old April 19th, 2017, 10:34 AM   #9
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 429
From the way it was posted I take it that they were energizing a 120Vac output and only reading 87V at the receiving end in another building.
Baring voltage loss due to wire resistance ( if it's just signal there would no voltage drop )Then it's clear to me that the 2 building are at different ground potentials.
this is why all points in an electrical system must be grounded to same point.
if the 2 building have a separate service then you must isolate the 2 systems
if they get connected together there could be big problems
  Reply With Quote
Old April 19th, 2017, 10:41 AM   #10
Ron Beaufort
Lifetime Supporting Member
United States

Ron Beaufort is offline
 
Ron Beaufort's Avatar
 
Join Date: Jul 2002
Location: Charleston, SC
Posts: 5,271
you gotta know when to hold 'em - and know when to fold 'em ...

well, the OP didn't tell us whether the output was OFF or ON when he got that 87V reading - so the "ground" issue might certainly be correct ...

and ...

he didn't tell us whether the "input" on the other end was regarding the 87V reading as an ON or an OFF signal ...

and ...

he didn't tell us which end of the wire the 87V reading was taken from (output module end - or input module end) ...

but ...

I've just got a "hunch" that it's leakage current - and since I'm not betting much, I'll stand ...
__________________

2-B ?
Best regards, ----+----] [----+------------( )----
Ron | |
PLC Training Boot Camp | 2-B |
+----]/[----+

I once was lost, but now am found, was blind, but now I see.


Last edited by Ron Beaufort; April 19th, 2017 at 10:47 AM.
  Reply With Quote
Old April 19th, 2017, 10:59 AM   #11
Bit_Bucket_07
Member
United States

Bit_Bucket_07 is offline
 
Bit_Bucket_07's Avatar
 
Join Date: Feb 2013
Location: Southeast US
Posts: 1,103
Quote:
Originally Posted by Ron Beaufort View Post
well, the OP didn't tell us whether the output was OFF or ON when he got that 87V reading - so the "ground" issue might certainly be correct ...

and ...

he didn't tell us whether the "input" on the other end was regarding the 87V reading as an ON or an OFF signal ...

and ...

he didn't tell us which end of the wire the 87V reading was taken from (output module end - or input module end) ...

but ...

I've just got a "hunch" that it's leakage current - and since I'm not betting much, I'll stand ...
I agree, but if it is a ground potential issue, then an interposing relay in the "input panel" with both the output and the neutral sourced from the "output panel" would resolve the issue.
__________________
  Reply With Quote
Old April 19th, 2017, 07:16 PM   #12
danw
Member
United States

danw is offline
 
danw's Avatar
 
Join Date: Oct 2004
Location: midwest, USA
Posts: 2,606
Quote:
Originally Posted by SoftwareJanitor View Post
from one building to another.
100 yards?
quarter mile?
half mile?

24g CAT5 cable?
  Reply With Quote
Old April 20th, 2017, 12:16 PM   #13
SoftwareJanitor
Member
United States

SoftwareJanitor is offline
 
Join Date: Dec 2016
Location: Southeast
Posts: 93
Call off the calvary...

As I've explained previously, I'm not a PLC guy, so I guess this was a false alarm.

It's a ControlLogix L73.

The card is a 1756-OW16I, 10-265V AC, 5-150V DC Isolated Relay.

The run between buildings is 300-400' ??

It was reading 87 volts with the signal OFF.

I had forced it ON in the PLC, but it really wasn't "ON" until I realized I had to "enable all forces" to make the "ON" turn red in the ladder. I *knew* I had the right point, and I saw the "ON" appear on the ladder output when I forced it, but didn't know it wasn't active until it turned red! Oh well!

Thanks for the quick replies, though ...
  Reply With Quote
Old April 20th, 2017, 12:52 PM   #14
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 9,782
Just to confirm what others have said. Your module does have a leakage spec, see pdf.
Attached Files
File Type: pdf leakagespec.pdf (119.6 KB, 25 views)
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old April 20th, 2017, 01:40 PM   #15
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 429
Let me follow up with this
the output is an OW16 card that's a relay output ( NO leakage)
if you were reading 87V at the receiving end with the output ON forced or otherwise then you have a serous grounding problem that needs to be addressed.
if you are reading 87V with the output OFF then you have some other serious problems with your system the needs to be addressed ASP. because you have a floating voltage someplace this floating voltage can kill you.
as for leakage, all solid state devices leak when off and the have a voltage drop across them when turned ON the current through them and the voltage drop when ON causes the heat in the device ( Heat is a bad thing here )
That's why they are called semiconductors ( Never fully ON and Never fully OFF)
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
ControlLogix Add-On instruction input and output behaviour Question thefatcontroller LIVE PLC Questions And Answers 10 November 21st, 2008 09:04 PM
Output Forces in ControlLogix mckeeal LIVE PLC Questions And Answers 1 October 23rd, 2007 06:42 PM
Data Echo in ControlLogix Output Modules Tayyab LIVE PLC Questions And Answers 2 July 2nd, 2007 12:01 AM
Forcing OFF josesaucedo LIVE PLC Questions And Answers 21 March 29th, 2007 03:06 PM
Setting Output Voltage on AB ControlLogix bcraig LIVE PLC Questions And Answers 15 June 18th, 2003 07:36 AM


All times are GMT -5. The time now is 08:52 PM.


.