plchacker
Hi all, it has been a while.
OK, I am setting up a process trainer with a 5/40E in an 8 slot chassis set up to single slot addressing. All is good so far. Group 4 in Rack 0 houses a 1771-IFE series A.
This is not my First run in with the old IFE modules. I have successfully set up many of these in the past.
It is set up for differential inputs. (Personal preference)
It is set up for 4-20mA. 0-4095. (Temporary until I get it working correctly)
It is set up for 2's complement.
LAD 2 has a single rung, JSR to LAD 3 which contains the BTR and BTW instructions for the three analog cards in the chassis.
The very first thing I did in this project was to set up the I/O config, and from there set up the cards/Logic for the cards. So there should be no corrupt data. Nothing in the program to interfere with the inputs/block transfers etc.
So the card works, I get a signal that fluctuates slightly when connected to a loop calibrator. Not as steady as I would like but not bad.
Next step, connect a Rosemount 3144P Temp Transmitter, (J-Type thermocouple) and 24VDC power supply. As soon as I powered up, and set up the transmitter the input started jumping wildly from 0 to a little over the signal value.
I do not have the empty channels shorted to common, as I have not yet connected all of the inputs I plan to use. Still, I have never seen a signal jump around like this.
The actual 4-20 signal is as steady as a rock.
I suspect noise, but at this point the PLC/Cabinet is pretty bare. The only I/O connected is the single transmitter to the IFE card. Any suggestions?