Problem Saving Channel Settings on AB 1771-IFE PLC5

hardaysknight

Lifetime Supporting Member
Join Date
Dec 2015
Location
Southeast USA
Posts
117
I'm having issues saving the individual channel settings on a 1771-IFE Analog card.



We recently swapped from 0-10v to 4-20ma transducers. I set the jumpers on the card, and set up the channel config in RSLogix5 and it works great, but any time the PLC is powered off/faulted/swapped to program mode, it goes right back to having a 0-10v channel configuration, throwing off our transducer readings.


This card is in a remote rack via controlnet

1771-IFE.png
 
Is this not right?


I'm gonna be honest with you, I have no idea what I'm doing.




EDIT: I figured it out. We aren't using a BTW to write the settings. We are using MOV instructions for each individual integer for the card configuration. No idea why.

1.png 2.png
 
Last edited:
You got it. I didn't notice you were using ControlNet. Local or expansion rack would have been block transfer.
 

Similar Topics

Ok, so yesterday I saw a new one (for me anyways). I'm writing a program that I've been working on for the last few weeks. I always make a habit...
Replies
9
Views
4,345
Hi, I have made some changes to a step 5 siemens program and decided to create a new file .I had the original file open(B2K1@@PX.INI) and went to...
Replies
6
Views
2,193
On all pages of my project i have a lot of information, texts and details that should not not be shown. I can remove them for each part apart from...
Replies
0
Views
40
Hi, I have had problem with upgrading some projects from v16 to v18. I tried it on 3 diffrent computers. I want to post this so that anyone that...
Replies
3
Views
170
Hi, I am having a challenge installing a new drive ACS355-03E-44A0-4 as it keeps on displaying Fault code F00018 even when the load is not...
Replies
3
Views
135
Back
Top Bottom