I'm having issues saving the individual channel settings on a 1771-IFE Analog card.
We recently swapped from 0-10v to 4-20ma transducers. I set the jumpers on the card, and set up the channel config in RSLogix5 and it works great, but any time the PLC is powered off/faulted/swapped to program mode, it goes right back to having a 0-10v channel configuration, throwing off our transducer readings.
This card is in a remote rack via controlnet
We recently swapped from 0-10v to 4-20ma transducers. I set the jumpers on the card, and set up the channel config in RSLogix5 and it works great, but any time the PLC is powered off/faulted/swapped to program mode, it goes right back to having a 0-10v channel configuration, throwing off our transducer readings.
This card is in a remote rack via controlnet