Old December 6th, 2017, 10:28 AM   #1
lesmar96
Member
United States

lesmar96 is offline
 
Join Date: May 2017
Location: PA
Posts: 124
deep well pump tripping on low current fault

One of our customers is a municipial water authority. They have several deep well pumps. The one well pump is on a vfd to slow it down because they put a new pump in and it pumped way too fast.

They also have a plc that monitors the amperage of each of the well pumps and will fault out if the pump current gets too high or too low. Each winter, we have the issue where the plc will start throwing a fault for low current on the pump with the vfd. It will work fine all summer long, but on some of the cold days and weekends, it will trip out sometimes a couple times a day.

What we are trying to figure out is what would cause the pump to pull low amperage when it is cold. Naturally, we would assume it could be running out of water, but why does that change when it is cold?

From the vfd to the pump is approx. 500' but we have filtering etc. This is basically the only issue we have with this. Any suggestions what we should check or upgrade?
  Reply With Quote
Old December 6th, 2017, 10:45 AM   #2
bright676
Member
United States

bright676 is offline
 
Join Date: Nov 2012
Location: va
Posts: 328
Too cold, Ice?
  Reply With Quote
Old December 6th, 2017, 10:54 AM   #3
lesmar96
Member
United States

lesmar96 is offline
 
Join Date: May 2017
Location: PA
Posts: 124
Quote:
Originally Posted by bright676 View Post
Too cold, Ice?
How would ice cause it to trip on low current? I figured if there was too much ice and the pump would lock up, we would have high current? The well is too deep for the water to be frozen.
  Reply With Quote
Old December 6th, 2017, 11:03 AM   #4
JohnCalderwood
Member
Scotland

JohnCalderwood is offline
 
Join Date: Feb 2014
Location: Stirling
Posts: 499
Is the impeller coming loose when it is cold?

Less load on the motor shaft....
  Reply With Quote
Old December 6th, 2017, 11:13 AM   #5
Rob...
Member
United Kingdom

Rob... is offline
 
Join Date: Jul 2016
Location: Manchester
Posts: 35
Impeller is just spinning surrounded by ice. Not drawing any load other than that necessary to spin the motor.

Or the pipe work has frozen, dependent on the type of pump, it may be happy sitting there pumping against a dead head rather than up to a 500' head. Although high lift pumps I've worked on need a head and somewhere to pump to otherwise they will trip on over current. Charging the lines with water was always fun.

If it was cold water there you would expect slightly higher current readings as water gets denser. (Then less dense as it crystallizes)
  Reply With Quote
Old December 6th, 2017, 11:19 AM   #6
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 51
I = V/R, as it gets colder, resistance increase, therefore current decreases.

This is a complete guess.
  Reply With Quote
Old December 6th, 2017, 11:24 AM   #7
mendonsy
Member
United States

mendonsy is offline
 
mendonsy's Avatar
 
Join Date: Feb 2009
Location: Western NY
Posts: 690
Lower ambient temperature = higher efficiency = less current draw
  Reply With Quote
Old December 6th, 2017, 11:34 AM   #8
alive15
Member
United States

alive15 is offline
 
Join Date: Oct 2015
Location: al
Posts: 51
I = V/R, lower voltage, so lower current; resistance stays the same ??
  Reply With Quote
Old December 6th, 2017, 11:57 AM   #9
BryanG
Member
United Kingdom

BryanG is offline
 
Join Date: Feb 2005
Location: Manchester
Posts: 1,138
You need to be logging the normal current and the lowest current so that you can see how bad the problem is. If it is borderline OK then you might need to adjust your current trip level. If it is a sudden current drop then you are looking at other problems including wiring issues (copper shrinks as it gets cold). You need data to find and solve problems, otherwise it is all just guesswork.
  Reply With Quote
Old December 6th, 2017, 01:16 PM   #10
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 578
Ice really. The frost line in Pa. is about 18" (deep well pump) I m guessing at least 100' or more. I know a lot that are much deeper then that. the water temp will be about 50 year round.
monitor and chart the motor current. less amps means less load, less volume or less pressure. is it possible that for winter they open a bleeder valve to keep some water flowing over the winter to keep the above ground pipes from freezing lowering the static pressure on the system
the water table could be dropping over the winter and caveating the pump but with all the rain we have had in Pa this year I really don't think the water table dropped this year I know placed that it's higher then normal.
how are you measuring the motor current ?
also Pa. hasn't had any days cold enough to freeze yet I don't expect it to jet that cold until about mid Jan.

Last edited by GaryS; December 6th, 2017 at 01:19 PM.
  Reply With Quote
Old December 6th, 2017, 01:53 PM   #11
lesmar96
Member
United States

lesmar96 is offline
 
Join Date: May 2017
Location: PA
Posts: 124
Yes, Gary, this pump is around 120', I believe. I do not think ice or water temp is the issue.

We are monitoring the current with a analog CT reading to the PLC. I have double-checked the accuracy of this and the CT seems to be reading accurately. A graph of motor current would be very helpful for troubleshooting. I will see about adding that to the program.
  Reply With Quote
Old December 6th, 2017, 01:59 PM   #12
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 1,311
In a centrifugal pump, load = flow. No flow = no load, no load = low current. The entire PURPOSE of monitoring for low current is in fact to detect when the flow is blocked. The icing could be happening anywhere in the pipe system.
  Reply With Quote
Old December 6th, 2017, 02:05 PM   #13
kekrahulik
Member
United States

kekrahulik is offline
 
Join Date: Apr 2009
Location: Lancaster,pa
Posts: 222
Can't see well water changing temp more than a smidge.

Do you have any data on pressure and flow. My guess is that something is happening to drop the backpressure on the pump (some one opened a valve somewhere etc) and with it, the amps drop.

How long does it need to be low amps before the alarm is set?
  Reply With Quote
Old December 6th, 2017, 02:45 PM   #14
GaryS
Member
United States

GaryS is offline
 
GaryS's Avatar
 
Join Date: Aug 2003
Location: Lancaster Pa.
Posts: 578
One thing I should have caught the first time.
you can't use a CT on the motor leads of a motor driven from a VFD to monitor the current the will always give you bogus readings CT's are designed to work with 60hz sign wave neither of these are produced in the output of a VFD.
if you want to monitor the motor current us the analog output for the VFD it will be much better then you will ever get with a CT.
I still don't see what the time of the year has to do with the load on the pump. there has to be something outside of the pump causing the flow to change
  Reply With Quote
Old December 6th, 2017, 03:27 PM   #15
g.mccormick
Member
United States

g.mccormick is offline
 
Join Date: Jul 2012
Location: IN
Posts: 419
Is it as simple as water demand/usage decreases in the winter time? Less demand means less flow means less current? And I also agree that standard CT may not work well on vfd. Using analog out from vfd would be better choice
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Neura Heat Pump Inverter Fault jimlong LIVE PLC Questions And Answers 8 May 11th, 2015 08:32 PM
program fault handler jude LIVE PLC Questions And Answers 21 February 19th, 2011 08:13 AM
RSLogix User Fault Routine jthornton LIVE PLC Questions And Answers 17 October 23rd, 2008 02:55 PM
TP177B + S7-300 on Profibus: No output happyhippo LIVE PLC Questions And Answers 23 May 15th, 2008 06:31 AM
Logic of Standby pump Shabbir LIVE PLC Questions And Answers 5 August 9th, 2002 11:00 PM


All times are GMT -5. The time now is 02:42 PM.


.