OT: High-Leg 240 ground fault relay. Who makes one?
jdbrandt
Oct 2002
Pennsylvania
1,203
I have a 240, 3 phase High-Leg power feeding a control panel.
Since there are heaters without Ground Fault Equipment Protection, there is a need for a Ground Fault alarm.
Does anyone know of a source for such a device, with the unbalanced (to ground/neutral) voltage that is present on this arrangement?
Also known as 'B phase', or 'Stinger Phase', or 'Orange Phase' to some of the other old timers here.
Thanks, guys.
Try Bender
Have a look at Bender. They should have something which will do the job. They have Ground Fault Monitors for grounded 3 phase systems with both internal and external CTs. I have used some of their products successfully.
If it is straight 3-phase with no neutral, then a GFCI shouldn't care about the voltage difference on the high leg (we call it a 'red leg' system here).
I'm not familiar with 3-phase GFCIs, but I would think it just senses an imbalance of current like the single-phase ones do... :confused:
-Eric
I would think like Eric that any GFCI would work that same way. Normally, all currents should mathematically sum to 0 (considering directional flows). If not, then somewhere there is a leakage to ground. As long as a GFCI is rated to handle the maximum voltage, then the currents should not be a problem.
I know this has come up many times but I've yet to hear a good way to deal with the vfd issue. Here's where I am. I have a very old Haas milling...
31
12,065
What is the US standard color coding of the high leg and other phases in a delta circuit? TIA This is what I have:
3,516
I work in a plant that has a High Leg Delta electric service, very old plant... we are having several VFD's tripping on bus overvoltage, across...
26
7,077
Not really my problem, but my city has asked for help. They have two 15 hp 230V 3-phase motors pumping make up water into their water tower. The...
10,023
Do i have to use interrupt subroutine, or immediate read high speed input, for Unitronics Samba plc or reading only the correponding register in...
124