Siemens S7 w/ Modicon I/O ???

I am preparing to upgrade our plant HMI and PLC systems. Currently we use Modicon 984-785E PLC and Modicon remote I/O. Due to HMI considerations, I really want to use Siemens software which requires Siemens PLC. I have been told its possible to keep the existing Modicon I/O and talk through the 785E to the S7? Due to the costs associated with changing the I/O to Siemens, this solution would be nice.

Can anyone offer any information on this subject?
  Reply With Quote
Old December 26th, 2002, 10:54 AM   #2
Jim Dungar
Member
United States

Jim Dungar is offline
 
Join Date: Apr 2002
Location: WI
Posts: 1,152
Most HMI packages have drivers that allow communication to almost all major PLC vendors. Why do you need to change you Modicon processor to Siemens? Do you want your S7 to be your logic controller or simply a data concentrator?

I am not aware of any device that would allow an S7 device to talk directly to Modicon I/O.

One option is to install a gateway that allows the Modicon 785E to speak Siemen's protocols. One manufacturer is ProLinx at http://www.prolinxgateways.com/ they have Modbus and Modbus Plus capability. The logic in the Modicon stays where it is and your HMI thinks it is talking to a Siemens PLC.

Another option is to install an S7 processor that passes data back and forth to the Modicon. This method would require the S7 to have a Modbus or a Modbus Plus port. With this option, you can move the logic control to the S7 and have the Modicon just be an I/O servicer.
  Reply With Quote
Old December 26th, 2002, 01:25 PM   #3
estover
Member
United States

estover is offline
 
estover's Avatar
 
Join Date: Jun 2002
Location: York, PA
Posts: 8
Thanks for the reply.

I need a Siemens PLC because the Siemens software package requires it. I am interested in a specialty version of Siemens PCS7 software. It does both SCADA controls on the HMI side and logic control for the PLC all in one.

I think your mention of using the S7 for control and the 785E as an I/O "gateway" is what I have heard before. Are there any concerns about doing this?
  Reply With Quote
Old December 27th, 2002, 10:50 AM   #4
Jim Dungar
Member
United States

Jim Dungar is offline
 
Join Date: Apr 2002
Location: WI
Posts: 1,152
You need to consider what will happen to your I/O if there is a loss of communications.

One scenario:
S7 is reading the Modicon inputs, there probably won't be any problems, loss of communications = S7 sees all inputs as off.

S7 is writing to Modicon outputs, there is the probablity of dangerous operation, loss of communication = Modicon leaves all outs in last state.

You need some type of communications monitoring logic in the Modicon. This logic should turn off all of the outputs. Also, don't forget the Siemens needs to know that the communications link failed.
  Reply With Quote
Old December 27th, 2002, 01:28 PM   #5
estover
Member
United States

estover is offline
 
estover's Avatar
 
Join Date: Jun 2002
Location: York, PA
Posts: 8
good point!

Thanks for the tip.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Controllogix elledge LIVE PLC Questions And Answers 43 February 12th, 2014 03:55 AM
SCADA with S7 PLC by means siemens S7 PC/MPI cable Andoni LIVE PLC Questions And Answers 4 December 15th, 2008 08:04 PM
Siemens S7 Ethernet Problem S7Guy LIVE PLC Questions And Answers 7 February 4th, 2008 03:51 PM
Siemens S7 ethernet protocol fzhang LIVE PLC Questions And Answers 3 May 19th, 2004 01:06 PM
AB panelView Plus MMI with Siemens S7 314 iknowsomeplc LIVE PLC Questions And Answers 0 November 18th, 2003 01:52 AM


All times are GMT -5. The time now is 12:09 PM.


.