We am planning to build an electrical enclosure on the manufacturing line. The only concern is to prevent dust from getting collected inside the enclosure. We will be providing with an pulsating airflow from the top of the enclosure to blow of the dust. With respect to the airflow, what are the things that we need to consider? What kind of air filter or pressure regulator do we need?
|
![]() |
![]() |
#2 |
Lifetime Supporting Member
![]() ![]() Join Date: Nov 2011
Location: Corona, CA
Posts: 2,038
|
Are you planning on using an Exair unit or equivalent?
https://www.exair.com/n12cc.html These systems come with or give recommendation of type of filter and pressure regulator. If the cabinet stays at positive pressure, of even a few inches, you will be okay. Don't think you need pulsating airflow, and it may be detrimental.
__________________
****Control Freak**** Net is where I be and Nathan is me. I have a condition called "The Knack". https://www.youtube.com/watch?v=g8vHhgh6oM0&t=2s |
![]() |
![]() |
#3 |
Member
|
I would go with these
Thermoelectric Air Conditioners, cold plates, liquid chillers, Peltier coolers First I would recommend you use a NEMA 4 enclosure even though it is inside the plane the NMA 12 will still leak I would avoid any device that uses the plant air compressor air Plant Air always has oil in the compressed air that oil will eventually end up coating all the components in the panel and make a real mess. I have seen those used many times and they always end up with the oil and dust coating everything. With the Teca units there is no outside air exchange so everything stays clean |
![]() |
![]() |
#4 | |
Lifetime Supporting Member
![]() ![]() Join Date: Nov 2011
Location: Corona, CA
Posts: 2,038
|
Quote:
Thermoelectric is the way to go, but depends on heat generated in cabinet can make them costly. It is okay for the Nema 12 to leak some as long as cabinet is slightly positive pressure. If Nema 4 enclosure, you would not have to worry about dust anyway...
__________________
****Control Freak**** Net is where I be and Nathan is me. I have a condition called "The Knack". https://www.youtube.com/watch?v=g8vHhgh6oM0&t=2s |
|
![]() |
![]() |
Bookmarks |
Currently Active Users Viewing This Thread: 1 (0 members and 1 guests) | |
Thread Tools | |
Display Modes | |
|
|
![]() |
||||
Thread | Thread Starter | Forum | Replies | Last Post |
Powerflex 525 STO button inside enclosure | mylespetro | LIVE PLC Questions And Answers | 15 | October 14th, 2020 06:36 PM |
Arc Flash Enclosures (inside Flange enclosure) | Rson | LIVE PLC Questions And Answers | 11 | May 22nd, 2019 09:58 AM |
Looking for an instrument, dust detection. | PLC Pie Guy | LIVE PLC Questions And Answers | 16 | March 26th, 2019 07:22 PM |
dust and ammoniac problem in electrical room | Lesa | LIVE PLC Questions And Answers | 8 | August 28th, 2008 07:38 AM |
Mounting a speed pot inside an enclosure | jlgluck | LIVE PLC Questions And Answers | 5 | December 11th, 2007 04:42 PM |