Hello,
a while back ago i posted a question about device net communications between an allen bradley PLC5 and a micro motion flow meter. I never went back to that post because i was severely under informed with device net and would have just wasted peoples time.
after diving into the subject more i now have a good grasp of whats going on but still have a question. I have a device net network where i have a flow meter on node 63 that sending data to the 1771-sdn modules input table. the PLC5 reads/writes the data with BTR/BTW instructions.
when i look at the scanner card properties, i see that its using a block transfer 62 to pull the data in from the flow meter. the data is 21 bytes long so the input setup tab shows a total of 168 bits being pulled in. what i dont see here is where the data is coming from.
i started to look at the micromotion flow meter in rsnetworxs and pulled out the EDS file and saw where the data is coming from. there is a group of data called input 6 that is 21 bytes long so i understand where 168 comes from.
now here is the issue, there is more data that i want to bring in that does not reside in input 6, there is another group input 7 that is also 21 bytes long that has the additional data.
how can i bring in two sets of input data into the scanner card so its accessible to my plc? i am writting this post away from my work computer so im trying to recall as much from memory after a long day so i can clarify any questions that arise.
thanks
Ricardo L.
Can you post a link to a user manual for the MicroMotion, or its EDS file ?
Unfortunately you have probably identified a situation where you can select a particular "assembly" of data to be part of the I/O connection, and in general you can't connect to more than one Assembly at a time.
The other technique for reading data that's packed into an Assembly is to send an "explicit message" to the device. That's a non-trivial task with the old 1771-SDN, but it's possible.
Hello Ken,
thanks for your reply. I have attached the EDS file and also a screenshot of the parameters for the flow meter and scanner on rsnetworx. Looking at the parameters, i see that parameter #7 is the one that is setting the group of variables to make available for the scanner.
In the meter's parameter tab, there exists poll info and cyclic info where it appears i can select a set of input data for each one. i also see the same terms in the scanners scanlist tab when selecting the edit I/O parameters of the flow meter and currently only the polled option is selected. In RSnetworx, If i were to set the cyclic info parameter for the meter to reflect the second set of data that i need, could i select the cyclic box in that scanner parameter tab and map both sets of data?
  • RSI_EDS_Micro Motion Model 2400S Rev 2.1.txt
Hello, I'm trying to setup a devicenet network using an AB 1769-SDN devicenet card with an Omron CJ1W-DRM21 device net card. The AB will be the...
2,010
I'm trying to use a micrologix 1500 with a 1769-SDN devicenet card to communicate to an Omron CP1H using the Omron CJ1W-DRM21 card. Does anyone...
2,175
I need to know if anyone has used an AB ControlLogix with a Devicenet Scanner to control the I/O in an Omron C200H? From what i can find I think...
3,109
I have a new install with a slc 5/03 and devicenet scanner. The network only has 1 node, a numatics valve bank. Is a 1770-KFD or 1784-PCD the only...
3,500
Hi. We've been asked to do an upgrade on plant, consisting on a PLC upgrade. This involves replacing a 1747-SDN module to a 1769-SDN, in a network...
65