Hi all,

I have a Watermaster with 4-20mA output and it needs to be hard wired to 3 different PLCs (due to client specific standards). The PLCs are controllogix & compactlogix. I ideally want these to go through a signal isolator/duplicator but I haven't come across a 1 in 3 out, only 1 in 2 out. Does anyone know of any? If not I assume the next best thing is to have the output of the watermaster going to multiple isolators/duplicators in a loop.

Thanks
 
Multiple loop isolators in series will work fine as long as the total input impedance doesn't exceed the maximum impedance the flowmeter can drive with its output (check the transmitter specs).

Most isolators will have a standard 250 ohm impedance, but i have come across some with 10 ohm and 100 ohm impedance.
 
Most 4-20ma outputs will drive at least 2 if not 3 in seties, I have done many systems where a 4-20ma transmitter is looped in series with a PLC & a chart recorder, I have even seen 3 but I'm a little wary of 3, so it would porobably be ok to loop the sensor to a PLC & a two output repeater so you have all 3, it will depend on the specs but never found a sensor that will not drive two, as it is 4-20ma there shuold not be any problem.
 
Other ideas:

If you have an AO card with three spares, you could use them to drive your other PLC's.

Another trick is to use Serial or Ethernet comms and reference the variable on the 'master' PLC that has the AI channel.
 
Other ideas:

If you have an AO card with three spares, you could use them to drive your other PLC's.

Another trick is to use Serial or Ethernet comms and reference the variable on the 'master' PLC that has the AI channel.
Yeah, anymore when stuff like this comes up I suggest a cheap PLC like an Automation Direct Click and use that as the splitter. Quite likely cheaper than a traditional splitter.
 

Similar Topics

I am not sure why this is requested, but it was asked. Currently I have one PLC , with one output to a relay, turning on a field equipment (just...
Replies
7
Views
217
Hi, I am working on automating an industrial fabric shrinkage tester to replace its outdated electronics with a PLC. To get the tank's water level...
Replies
14
Views
536
Hello, I have a compact Logix plc and I have been task with configuring alarms into our SCADA when an Analog signal stops moving. The analog...
Replies
6
Views
241
Hi I have an old panel builder 32 that I’m replacing for a factory talk me hmi . In the plc for the old panel builder there is a coms bit for the...
Replies
0
Views
74
I'm pretty new to PLC's, so forgive me if I use the wrong terminology and whatnot. We have an issue at work where we have a flow meter that is...
Replies
10
Views
291
Back
Top Bottom