NetNathan Lifetime Supporting Member N Join Date Nov 2011 Location Corona, CA Posts 2,199 Sep 5, 2018 #1 Does GE RX3i have a "Rate of Change" FBD or? I need to alarm on an analog signal that changes to fast or "Spikes".
Does GE RX3i have a "Rate of Change" FBD or? I need to alarm on an analog signal that changes to fast or "Spikes".
Sapper307 Member S Join Date Nov 2017 Location Maryland Posts 107 Sep 5, 2018 #2 There's no native rate of change function block or instruction that i'm aware of. Maybe some creative use of relational function blocks like compare, greater or equal, less or equal coupled with a timer? edit: also maybe something worth scripting
There's no native rate of change function block or instruction that i'm aware of. Maybe some creative use of relational function blocks like compare, greater or equal, less or equal coupled with a timer? edit: also maybe something worth scripting