Studio 5000 - strange error , "conflict exists in project verification state"
einnh
Mar 2014
New England
275
I am trying to upload a test project to our 5069 controller we use for development and am getting an error I haven't seen before:
"Error: conflict exists in project verification state"
There are no specifics, it isn't a linked error that I can click on to see where the issue lay.
Google Searches are getting me nowhere.
Anyone run into this?
5069-L306ERS2 controller running v33
Have you done "verify the entire controller" ?
Do you see any Exclamation mark in Controller organizer? Like any hardware configuration that do not match?
Are you sure you mean upload?
We call it download to PLC, upload is getting program file from PLC to PC.
Have the BNOT_f in use?
https://compatibility.rockwellautomation.com/GeneratedReleaseNote.aspx?v1=58247&v2=58247&o=&pdf=0
Corrected anomalies for Studio 5000 Logix Designer, version 33.00.00
Conflict existed in project verification state
In a function block diagram routine, when working offline and adding a BNOT_f instead of a BNOT instruction, the Logix Designer application generated the error Conflict exists in project verification state. Internal error. Call Tech Support.
This anomaly first identified in version 32.00. (Lgx00227391, Lgx00227544)
Saw this error today while programming a L73S PLC. I fixed it by changing the controller type to a L72S then back to a L73S. Not sure how I caused it programming offline, but something must've reset by changing the controller type. Hope this helps.
This forum post I found seemed to reference the same issue, and if posts were still allowed on that thread, I might make an account there to post...
5,782
Hi Everyone. Not posted on here for a long time, but I am hoping someone can help me. I am doing a differential pressure calculation in a L27ERM...
Hi, how do I convert 2x Integer registers to a Real? The two integers are from Modbus registers that contain a floating point value, I need to...
104
What is the best way to extract the hour and minute from the register that comes from Yaskawa VFD. In studio 5000 I have a register saved as INT...
103
I have an Allen Bradley temperature switch that I am trying to use in studio 5000. I am getting the message "Unable to interpret the IODD file"...
64