UDP socket communication to PC with ControlLogix and 1756-EN2T

Hello,

I need to establish a UDP socket communication between a ControlLogix L72 PLC and a Linux-PC on the other side with a 1756-EN2T network card.

I have really no idea how to do this. I found nothing suitable in the AB library or knowledgebase.
Can anyone provide a sample program how to handle this?

Thank you so much in advance!

Stefan
  Reply With Quote
Unread November 8th, 2016, 11:46 AM   #2
jstolaruk
Lifetime Supporting Member
United States

jstolaruk is offline
 
Join Date: Dec 2004
Location: Detroit, SE Michigan
Posts: 3,448
PM sent
__________________
"You can live to be a hundred if you give up all the things that make you want to live to be a hundred." Woody Allen
  Reply With Quote
Unread November 8th, 2016, 12:31 PM   #3
Contr_Conn
Member
United States

Contr_Conn is offline
 
Contr_Conn's Avatar
 
Join Date: Sep 2003
Location: Ohio
Posts: 2,091
Since your question is very generic, I can only recommend you to start with the Logix Sockets user manual enet-at002
http://literature.rockwellautomation...t002_-en-p.pdf
and technote 32962

there are plenty of examples in the knowledgebase
  Reply With Quote
Unread November 9th, 2016, 01:49 AM   #4
taylor1982
Member
Germany

taylor1982 is offline
 
Join Date: Aug 2011
Location: Bavaria
Posts: 71
Thanks for your replies.

Due to this I have a view questions:

- I need to implement a very fast connection so I need to send and receive as fast as possible. How ist the best way to trigger the READ and WRITE message instructions?
- Can READ and WRITE be triggered at the same time?
- How do you usually trigger the instructions? With a fast toggle bit and the negated .DN-Bit before the message instruction?

Thank you!
  Reply With Quote
Unread November 9th, 2016, 12:21 PM   #5
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,993
Quote:
- I need to implement a very fast connection
If so, use cyclic I/O instead of raw sockets and UDP.

The best way to do this is to buy a Linux EtherNet/IP Adapter software product, or try the open-source OpENer project:

https://github.com/EIPStackGroup/OpENer
  Reply With Quote
Unread November 10th, 2016, 01:34 PM   #6
taylor1982
Member
Germany

taylor1982 is offline
 
Join Date: Aug 2011
Location: Bavaria
Posts: 71
Quote:
Originally Posted by Ken Roach View Post
If so, use cyclic I/O instead of raw sockets and UDP.
Unfortunately this is no option. On the other side is a Linux PC and the customer want to use UDP sockets.

Any suggestions?
  Reply With Quote
Unread November 10th, 2016, 01:40 PM   #7
marshg
Member
United States

marshg is offline
 
Join Date: Oct 2003
Location: Carmel, Indiana -->Reno, NV soon!
Posts: 5
Due to this I have a view questions:

- I need to implement a very fast connection so I need to send and receive as fast as possible. How ist the best way to trigger the READ and WRITE message instructions? I usually use an XIO |\| for the message enabled and then use a timer done bit XIC | | in series that pulses every 50msec or 100msec. The TON instruction would use an XIO |\| for the timer done in front of TON instruction. From my experience, only using the |\| Enable bit will cause the message instruction to hang sometimes. Make sure to use the done bit in series. Sorry, I don't use Rockwell at my current job so I hope the example shows up correct.
Msg.EN Tmr.Dn
|\|---------| |-----------MSG Instruction called Msg

Tmr.Dn
|\|-----------TON Instruction called Tmr

- Can READ and WRITE be triggered at the same time? Yes. The EN2T can hold up to 256 connections if I remember correctly. You can log into the EN2T card by typing in its IP address to see the maximum number of connections. You'll want to monitor this.
- How do you usually trigger the instructions? With a fast toggle bit and the negated .DN-Bit before the message instruction?

Thank you!
  Reply With Quote
Unread November 10th, 2016, 05:23 PM   #8
Contr_Conn
Member
United States

Contr_Conn is offline
 
Contr_Conn's Avatar
 
Join Date: Sep 2003
Location: Ohio
Posts: 2,091
Unfortunately answers in the post above are incorrect and misleadng
The rules above do not apply to sockets
You cant do socket read and write at the sametime
And performance really depends on the socket serice timeout as Msg reads the buffer and not the actual udp stream
  Reply With Quote
Unread November 10th, 2016, 06:06 PM   #9
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,993
Quote:
Unfortunately this is no option. On the other side is a Linux PC and the customer want to use UDP sockets.
Then change the customer's expectations.

ControlLogix cyclic I/O connections are fast, bi-directional, and use UDP. That sounds good to me.

You will almost certainly not get the performance you want from the raw sockets feature of the 1756 Ethernet modules.
  Reply With Quote
Unread November 19th, 2019, 11:29 AM   #10
BachPhi
Member
United States

BachPhi is offline
 
Join Date: Dec 2007
Location: Los Alamos
Posts: 337
Quote:
Originally Posted by Ken Roach View Post
If so, use cyclic I/O instead of raw sockets and UDP.

The best way to do this is to buy a Linux EtherNet/IP Adapter software product, or try the open-source OpENer project:

https://github.com/EIPStackGroup/OpENer
Does RTA 490NBX count as a fast Linux EtherNet/IP Adapter?
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Controllogix 1756 & 1492-IFM40F-F120-2: Force a bit leonlai LIVE PLC Questions And Answers 9 September 17th, 2015 04:26 PM
ControlLogix Communication Help MattEveritt6 LIVE PLC Questions And Answers 3 February 18th, 2014 12:09 PM
Communication between AB Panel View Plus 1500 and 1756 controllogix controller wonderful_plc LIVE PLC Questions And Answers 17 January 26th, 2011 09:45 PM
ControlLogix 1756 Series A and B HNguyen LIVE PLC Questions And Answers 3 January 5th, 2008 08:40 AM
AB ControlLogix 1756 comm. HNguyen LIVE PLC Questions And Answers 7 July 13th, 2007 05:58 PM


All times are GMT -5. The time now is 05:43 AM.


.