Equivalent Block in Rslogix 5000 Function Block
androcci
Dec 2018
New Jersey
Hello, I am struggling to find a block that does the exact same thing.
the A/M block has everything a PID has except for the CV and PV.
the (A) input receives an analog signal from a PID output. if is in automatic then [(A) = output] of the A/M Block
If I use the PID then if I put it in automatic I will modulating about the SP and I dont want that.
the TC input if TC=1 then the output will equal the TV input
if the user press the button to go in manual it will just take that input.
I know that the TC & TV is the same as the CVinitreq & CVinitValue.
but I cannot find a way to have a block with selection of Manual and also have a second input to by pass it to the output.
Pretty much I need an block that;
Makes the output= input
takes manual input from the operator which I know I can just tag it. I hope I am making my problem clear. I know I cant do it wit the PIDE.
THANK YOU so much in advanced guys.
I am using my phone. So can’t open.
But. If you don’t need a PID loop. Then why not look separately at the existing output value.
Am I understanding this is what you want. Just a digital output greater or equal than a set point.
Hello to all, I know there are a few people here very experienced with Codesys. I wonder does Codesys have something similar to OB35 in STEP7...
624
I figured out a solution to a vfd issue... at least in theory. Yaskawa has a program called Drive Works EZ that you can have PLC-type functions...
3,846
Does anyone know the S7 equivalent of the Mitsubishi Q-Series command PLF? PLF is a one-cycle pulse on the falling edge of the input signal. See...
557
Is there an equivalent Rockwell PLC NOP instruction that is available for the M340 M580 Schneider PLC? Thanks,
2,719
I used GSV to get the current status of older 1769 I/O modules. What is the equivalent for new 5069-I/O ? I know individual points/channels have...
1,018