PowerFlex 70 EC Not React to input and still in Not Enabled

philoux

Member
Join Date
Sep 2009
Location
Montreal
Posts
4
Hi, i recently install a powerflex 70 ec and still saying Not Enabled on the HMI... the safe off jumper is in place and the enlb jumper also. I also try a factory reset but still the same.
all digital input is set to not used exept the input #2 for Run ..... i have no more ideas about that trouble !!1


Thx
Phil
 
Check!

I Check the input configuration and all input is set to not used... i also check the jumper for the safe off is on pin 3-4.... but the strange think is is when i apply 24+ on input 6 (TB6) is saying Safe Off on the screen but the jumper is present on the safe off connector ???
 
Problem find!!!

I found the problem is located on the main board. Above the Safe Off connector the R108 Resistor blow up !!

Can find only the main board??? for replacement???
 

Similar Topics

Fairly new to the drive so apologise for the layman terms. Textile machine uses PF525 VFDs to control motors. The speed of the drive is currently...
Replies
5
Views
94
Hello Everyone, I want to upgrade the firmware of Powerflex 40 from 5.001 to 6.002 can anyone tell me how can I do that?
Replies
0
Views
57
Hello, I am currently in the final week of my internship and I have encountered issues with communication between a PowerFlex 700 variable...
Replies
8
Views
240
Hi there, I have above mentioned VFD which is communicating to my control logix(L62) plc using devicenet DNB scanner(plc side) and 20-comm-D card...
Replies
3
Views
184
Hi, I'm currently having issued with a PowerFlex 252. It was working fine last week, and suddenly decided to stop working. When I go into...
Replies
2
Views
126
Back
Top Bottom