OT: When is VFD cable recommended/required?

It sounds obvious, I know. The cost of good VFD cable for many motors over a modest distance is quite pricey.

The manuals say to always use a type of shielded cable rated for VFD applications.

In your experience, what requirements would an application have that require VFD type cable when using an induction motor and a VFD?

Always?
When motor HP is greater than X?
Cable length greater than X?

I ask because it seems to be excessively expensive and labor intensive to run VFD rated cable for many motors under 1HP, no more than 70’ from the cabinet.
__________________
“Did the Lord say that machines outta take the place of livin’, and what’s the substitute for bread and beans? Do engines get rewarded for their steam?” -John Henry

Last edited by seth350; May 30th, 2019 at 05:48 PM.
  Reply With Quote
Old May 30th, 2019, 06:03 PM   #2
James Mcquade
Member
United States

James Mcquade is offline
 
Join Date: Oct 2007
Location: Nashville, Tennessee area
Posts: 3,318
Before we go there, what voltage is the motors?
if 240v , no line / load reactors required.

if 440,460,480, then you need to install line and load reactor for motor leads longer then 25 ft - based on specs I read. the reflected power wave can go back into the plant power bus and create issues.

when using vfd's, you should use vfd rated motors. the motors are designed to work with vfd drives. standard motors can work, but will burn up faster.

you use shielded vfd cable to eliminate electrical noise, especially in control cabinets where the plc I/o are.

I will let other users chime in, please correct me if I an wrong.

james
  Reply With Quote
Old May 30th, 2019, 06:24 PM   #3
bulletin blues
Lifetime Supporting Member
United States

bulletin blues is offline
 
bulletin blues's Avatar
 
Join Date: Mar 2003
Location: out there
Posts: 216
Yesterday I downloaded a motors e-book included in a rockwell newsletter that had info on why to use vfd cable. You have to enter user info, but I don't think you need a tech connect.

https://info.plantservices.com/ebook...trical-systems
__________________
_____
  Reply With Quote
Old May 30th, 2019, 06:31 PM   #4
seth350
Member
United States

seth350 is offline
 
seth350's Avatar
 
Join Date: Jul 2011
Location: Over yonder
Posts: 372
Supply voltage we use is 480VAC and we do always use VFD rated motors with class F insulation with VFDs. I also have a line filter feeding the VFDs, no load reactors.

My question is generally when a project is spec’d, what makes you use VFD shielded cable versus the lesser?

We have OEM machines that have come in without VFD shielded cable on this project. I have spec’d a conveyor system using Belden 1000V VFD shielded cable for 24 0.5HP motors. The conveyors will transport product to and from all the other OEM machines.

Seeing their machines without the VFD cable made me doubt my decision.
In terms of dollars, was I correct to use the VFD cable over non shielded? Would I have cut a corner if I had not used the VFD cable?
__________________
“Did the Lord say that machines outta take the place of livin’, and what’s the substitute for bread and beans? Do engines get rewarded for their steam?” -John Henry
  Reply With Quote
Old May 30th, 2019, 07:01 PM   #5
bulletin blues
Lifetime Supporting Member
United States

bulletin blues is offline
 
bulletin blues's Avatar
 
Join Date: Mar 2003
Location: out there
Posts: 216
Well, in my experience, we had a motivated electrician who decided to replace about 20 standard overloads, all motors off of one drive, with the new and improved... I can't think of the term right now... "motor circuit protectors" over a weekend. They are all easily over 100 feet away, the furthest over 200 feet away. They are approximately 0.5 HP. Standard THHN through conduit. They were installed in the 1980's. The reason was that the existing overloads are located at the bottom of the cabinet and it is difficult to see which one is tripped, difficult to isolate etc. After replacement and testing, they all tripped randomly. Poor guy had to go back and re-install the originals. He's not as motivated any more.

I did some research and it appears that placing the overloads closer to the motor might have helped. Now that we're on the subject, maybe running shielded cable may help, but that will likely never get re-visited

That's my experience with NOT using VFD cable.

So, from my experience, be careful with the Motor Circuit Protectors, as they seem to be sensitive to longer distances.
__________________
_____
  Reply With Quote
Old May 30th, 2019, 07:13 PM   #6
dogleg43
Member
United States

dogleg43 is offline
 
Join Date: Dec 2005
Location: Indiana
Posts: 501
If the motor and or the VFD manufacturer recommends using VFD cable then I would use it. Otherwise, if tech support is required they will probably want to use the lack of VFD cable as being part of the problem.

Speaking from experience.
  Reply With Quote
Old May 30th, 2019, 07:33 PM   #7
rupej
Member
United States

rupej is offline
 
Join Date: Sep 2014
Location: NC
Posts: 938
Rockwell has a paper that talks about it. IIRC, it clearly stated that it wasn't necessary unless noise would cause an issue to neaeby devices. It did not suggest any risk to drive or motor by not using VFD cable.
  Reply With Quote
Old May 30th, 2019, 09:57 PM   #8
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 2,105
IMHO and experience you do not need shielded cable IF you use STEEL conduit and rigorously ground it (use grounding bushings, etc. etc.) and you use ONE CONDUIT RUN FOR ONE MOTOR (i.e. don't run the wires for 4 motors inside of one conduit run).

ANY other way of running the conductors will require shielded cable; PVC conduit, cable tray, duct banks, gutter etc. I've seen an installation where just 25ft of a 300ft motor run was coming out of the steel conduit, laying in cable tray (next to the input cables) and back into steel conduit to the motor, but in that 25ft of exposure it picked up enough induced voltage to cause damage to the windings of an inverter duty motor.

If the mfrs tell it to you in this way however, they can catch blame for a failure if you were not fastidious about your conduit run and grounding issues, so they just do a CYA statement telling you to always use shielded cable because although expensive and redundant, there is nothing wrong with shielded cable inside of steel conduit.

Also understand that for the VFD mfrs, the products are going everywhere in the world and in most of the world, they do NOT use steel conduit as much as we do here in North America, so for them, it is more important.

Last edited by jraef; May 30th, 2019 at 09:59 PM.
  Reply With Quote
Old May 30th, 2019, 10:53 PM   #9
dogleg43
Member
United States

dogleg43 is offline
 
Join Date: Dec 2005
Location: Indiana
Posts: 501
Jref, I agree with all of your points. As a system integrator we often just supply the VFD, controls, and do the programming (and are responsible for the VFD system working correctly). Usually the motor and field wiring are done by an EC who is subcontracted to the GC. So it gets tricky trying to convince them what type of field wiring to run.

We’ll normally forward to them in writing what the VFD manufacturer requires and tell them we can’t be responsible if things don’t work because they (EC) did not follow the suggested requirements.

Last edited by dogleg43; May 30th, 2019 at 11:11 PM.
  Reply With Quote
Old May 30th, 2019, 11:18 PM   #10
seth350
Member
United States

seth350 is offline
 
seth350's Avatar
 
Join Date: Jul 2011
Location: Over yonder
Posts: 372
Thank you jraef, I was hoping you would give your personal experience. I opted to use a steel wire basket with a separator for motor cable, I/O, and comms. Using the wire tray, I felt it was necessary to use a shielded cable for the motors. The IO and comms are also shielded.

So maybe I did a half decent job after all.
__________________
“Did the Lord say that machines outta take the place of livin’, and what’s the substitute for bread and beans? Do engines get rewarded for their steam?” -John Henry
  Reply With Quote
Old May 31st, 2019, 05:19 AM   #11
PLC Pie Guy
Member
Canada

PLC Pie Guy is offline
 
PLC Pie Guy's Avatar
 
Join Date: Jun 2013
Location: Halifax
Posts: 1,108
Steel conduit or teck at very least. But around here, I always have the guys use VFD cable if there is a drive involved. Just to many headaches over the years and replacing of motors, drives and other sensitive equipment in the areas... due to people using WTF ever is laying around to connect motors. Usually what they grab isn't even rated for our wet environment. The VFD cable is rated for our environment and I have yet to see a piece fail.

Also, its likely that whatever other cable you would use is likely only rated for 600V..... Not even close to the possible output you could see from today's drives! 600VAC in does not equal 600VAC out on a 3 phase drive!

We don't even have this conversation anymore. Its a no brainier. Especially if somebody else is footing the bill!

Last edited by PLC Pie Guy; May 31st, 2019 at 05:24 AM.
  Reply With Quote
Old May 31st, 2019, 06:16 AM   #12
Rson
Member
United States

Rson is offline
 
Join Date: Jun 2017
Location: Michigan
Posts: 482
Maybe it is just my industry, but I use cables / receptacles for every motor under 10 HP.

The Turck cables (I'll have to look up part numbers later) are pretty awesome and not super expensive. I think I pay about $150 for a cable, a receptacle for the panel, and a receptacle for the motor. Then you just plug-and-play.

Most of the time though, my motors are within 2-4 meters of my enclosure. Prices definitely get more expensive the further away the motor is.

Also, many times my enclosure ships separate from the machine, and I don't always want to leave wiring the motor to the end user. With the cable / receptacle combo, I can at the very least plug in the motor for testing before it leaves our facility. The $150 pays for itself in this convenience.

And, if it needs to be relocated, just buy a longer cable!
  Reply With Quote
Old May 31st, 2019, 09:08 AM   #13
seth350
Member
United States

seth350 is offline
 
seth350's Avatar
 
Join Date: Jul 2011
Location: Over yonder
Posts: 372
Thank you guys for sharing your experience. I feel much more confident.

VFD Cable = No Brainer
__________________
“Did the Lord say that machines outta take the place of livin’, and what’s the substitute for bread and beans? Do engines get rewarded for their steam?” -John Henry
  Reply With Quote
Old May 31st, 2019, 10:09 AM   #14
jraef
Member
United States

jraef is offline
 
jraef's Avatar
 
Join Date: May 2006
Location: Northern California
Posts: 2,105
Quote:
Originally Posted by PLC Pie Guy View Post
...
Also, its likely that whatever other cable you would use is likely only rated for 600V..... Not even close to the possible output you could see from today's drives! 600VAC in does not equal 600VAC out on a 3 phase drive! ...
Good point and I should have brought that up. Even if you use steel conduit, I now recommend using XHHW conductors, not THHN or THWN (on the OUTPUT side, input side doesn’t matter). You want Cross Linked Polyethylene (XLPE) insulation, not PVC (as is used in THHN) because PVC van have microscopic bubbles in the plastic that weaken the insulation capability in the face of higher voltage spikes in VFD outputs due to reflected waves. XLPE insulation is made differently, like heat shrink, so there are no bubbles or weak spots. That’s why you usually see it with 1000V or 2000V insulation ratings. It’s more expensive, but less expensive than replacing the cables later. Most good VFD cable will use XHHW for the conductor insulation, only the outer jacket might be PVC where it doesn’t matter.
  Reply With Quote
Old May 31st, 2019, 10:12 AM   #15
seth350
Member
United States

seth350 is offline
 
seth350's Avatar
 
Join Date: Jul 2011
Location: Over yonder
Posts: 372
Thank you jraef, I will remember that.
__________________
“Did the Lord say that machines outta take the place of livin’, and what’s the substitute for bread and beans? Do engines get rewarded for their steam?” -John Henry
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Advice on Selecting VFD Cable Tim Ganz LIVE PLC Questions And Answers 5 May 5th, 2017 09:19 PM
VFD to motor cable via plug/socket advice paraffin power LIVE PLC Questions And Answers 3 March 31st, 2015 04:52 AM
OT: Earth leakage current (VFD) Werner LIVE PLC Questions And Answers 9 June 12th, 2009 01:40 AM
OT: Motor / VFD question naegely LIVE PLC Questions And Answers 23 February 23rd, 2009 08:28 PM
Seimens VFD issue ascot01 LIVE PLC Questions And Answers 5 February 14th, 2009 11:19 PM


All times are GMT -4. The time now is 10:44 AM.


.