OT: When is VFD cable recommended/required?

Maybe it is just my industry, but I use cables / receptacles for every motor under 10 HP.

The Turck cables (I'll have to look up part numbers later) are pretty awesome and not super expensive. I think I pay about $150 for a cable, a receptacle for the panel, and a receptacle for the motor. Then you just plug-and-play.

Most of the time though, my motors are within 2-4 meters of my enclosure. Prices definitely get more expensive the further away the motor is.

Also, many times my enclosure ships separate from the machine, and I don't always want to leave wiring the motor to the end user. With the cable / receptacle combo, I can at the very least plug in the motor for testing before it leaves our facility. The $150 pays for itself in this convenience.

And, if it needs to be relocated, just buy a longer cable!

I should note - I just looked up the cables that I was mentioning (powerfast) and they are not shielded cables.
 
I should note - I just looked up the cables that I was mentioning (powerfast) and they are not shielded cables.

Thanks Rson, those cable and plug assemblies you mentioned were interesting. Too bad they are not shielded. I could have used them on another project.
 

Similar Topics

Hello, I've been trying to learn this a while now and still have not found out how this works. I have an Omron CJ2M PLC and an ABB ACS 355 VFD...
Replies
1
Views
253
I have a VFD rated for 125HP at 480V. After the VFD, there is a sine wave filter, then a 480/240 150KVA transformer, before the 100HP motor...
Replies
8
Views
3,191
We are looking into installing a well water pump (480vac, 25hp, 40FLA) with a PowerFlex 755 VFD. The challenge is that the well is located about...
Replies
13
Views
4,713
I am looking to use Lapp VFD cable and have configured it for the size I need in the attached file. But Which one of these 4 is the best choice...
Replies
5
Views
3,075
I need some help with properly sizing VFD cable for a AB Powerflex 755 drive at 65 amps output. Am I supposed to size for 65 amps 100% or should...
Replies
6
Views
3,047
Back
Top Bottom