1756-EN2T/EN2TR v10.010 anomaly
freshmeat
Sep 2017
China
Hi everyone,
I have a 1756-EN2T/D and 1756-EN2TR/C with firmware v10.010.
From the release note, there is an anomaly:
Ethernet module sends incorrect ARP at switchover (00194847)
Corrected Anomaly with Firmware Revision 11.001
Known Anomaly First Identified as of Firmware Revision 10.006, Catalog Number:
1756-EN2T/D
1756-EN2TK/D
Known Anomaly First Identified as of Firmware Revision 10.007, Catalog Number:
1756-EN2TR/C
1756-EN2TRK/C
1756-EN2TRXT/C
1756-EN2TXT/D
1756-EN3TR/B
1756-EN3TRK/B
Known Anomaly First Identified as of Firmware Revision 10.009, Catalog Number:
1756-EN2F/C
1756-EN2FK/C
Known Anomaly First Identified as of Firmware Revision 10.020, Catalog Number:
1756-EN2TP/A
1756-EN2TPK/A
1756-EN2TPXT/A
Ethernet module sends Address Resolution Protocol (ARP) to gateway address with source IP 0.0.0.0 at ControlLogix Redundancy switchover.
For some reasons, I cannot upgrade the firmware to v11.001.
Can anyone tell me what will be happen if the Ethernet module sends Address Resolution Protocol (ARP) to gateway address with source IP 0.0.0.0?
Thank you in advance.
Freshmeat
Switchover is only part of Redundancy System and FW 11 is not qualified to run v11 yet.
I recommend you to refer to the latest redundancy bundle.
Hi Contr Conn,
Thank you for your reply.
I apologize if I make you confused.
The redundant bundle I am using is v20.058kit2, which requests firmware of 1756-EN2T/D and 1756-EN2TR/C to be 10.010.
As the anomaly is fixed in 11.001, I cannot upgrade the firmware of EN2T & EN2TR to 11.001 unless I use another bundle.
But that will cause a lot non-technical issues.
Regards
So I have code to read the IP address of a 1756-EN2T with a MSG block - Get Single Attribute. Does anyone know where to find the MSG block...
1,141
I've been trying to get this Ethernet module configured to send emails to our relay server but cannot get it to work. the EN2T is running...
1,759
Dear All, I have been using 5561 CPU with redundancy, Few days ago, I have seen the message Disqualified on RM module of secondary PLC. and i can...
766
Good day folks, We have an L71 processor (v30.02) in a rack with an EN2T connected to the plant network & another (v10.007) used for IO only -...
2,136
I have a pair of 1756-L73 controllers on A4/A backplanes with PA72 power supplies, configured for redundant operation with RM2 and EN2T modules...
2,779