block transfers to panelview 550

hi guys, i have been through alot of the archives and have learned alot on the subject of the btr and btw instructions.
i have started not too long ago a new robotic cell that is going to be 90% rio. 2 ABB S4 robots with rio, 2 1791-IOBW rio block i/o and
1 panelview 550 with rio. A SLC 5/03 is the prossessor with a scanner card.

I have the robots and block i/o down pat. Now i am trying to grasp
the concept of btr and btw to a panelview when i am so used to dh-485 connection directly to the slc.

i have reserved the last logical rack "3" for the panelview
should i reserve the first 4 groups for btw
and the last 4 groups for btr ?

also all my data is in n60,n61,n62 and n63 files first 2 for outgoing
information and last 2 for incoming information from the panelview.

when i block transfer my outgoing info i can grasp assigning the buffer file, data file and control block but when it comes to requested word count would it be 2 and that would encompass both the 16 bits in the n60 and the 16 bits in the n61 file. So i could use 1 btw instruction to trasfer 32 bits of information at once.

anouhter thing, trying to use this information in the panelview.
i am used to just assigning tag addresses to correspond to the actual n60:1 or n60:2. will this still be the case?

when i btw all of n60 and n61 will it show up at the panelview as n60 and n61?

when i btr from the panelview, say push a momentary button and i write that to a tag which has an address of n62:1 do i just set up anouther buffer file and control block and data file to correspond to that n62 file?

these are probably pretty stupid questions but all i can find out there is examples in ladder logic and nothing showing the panelview program and how they address there tags.

could someone point me in the right direction?
thanks
mark
  Reply With Quote
Old February 15th, 2005, 10:55 PM   #2
Gerry
Member
New Zealand

Gerry is offline
 
Join Date: Jun 2002
Location: Auckland
Posts: 1,142
Are you sure you need block transfers?

If all you have is 32 bits each way, I would say no. Just use discrete addresses like I:030/2, etc. Note that for each 'module group' you will have 16 inputs and 16 outputs.

If you must use BTX, then only one group (0) is used. Read and write to this location with up to 64 words. If using multiple transfers, all BTR's must have unique lengths and all BTW's must have unique lengths.
Quote:
when i btw all of n60 and n61 will it show up at the panelview as n60 and n61?
Depends on how you set up the BTX in the PanelView. Easiest is to use the same addresses as in the PLC. You won't be able to transfer two files with one instruction.

Save yourself a lot of work and avoid the block transfers. The hardware combination you have must be the worst possible for doing BTX.
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
SLC 5/04 & PanelView 550 msinclair LIVE PLC Questions And Answers 8 April 23rd, 2006 02:42 AM
PanelView 550 Problem Tom Jenkins LIVE PLC Questions And Answers 15 August 16th, 2004 12:42 PM
How do I change a Panelview 550 RIO settings? mbalog LIVE PLC Questions And Answers 9 July 12th, 2004 04:21 PM
Not able to Communicate with Panelview 550 sanjay_snj LIVE PLC Questions And Answers 2 March 26th, 2004 06:55 AM
Block Transfer Sequencing Andrew Evenson LIVE PLC Questions And Answers 1 April 16th, 2003 02:27 AM


All times are GMT -5. The time now is 01:56 PM.


.