Air valve

I have this proportion air?
using 4-20MA command
I am using compact logix i have both analog input and DC Input cards?
do I also control the power through the PLC? to turn on and off?

Which card i am supposed to control the air valve? (analog or dc)?
cards # IQ16 & IF4
description below.
https://www.proportionair.com/litera...stallation.pdf
  Reply With Quote
Old March 12th, 2018, 03:12 PM   #2
padees
Member
United States

padees is offline
 
padees's Avatar
 
Join Date: Aug 2011
Location: Michigan
Posts: 437
You will need an analog output card to control the regulator. Just power it up with DC, don't have to go thru the PLC for power supply. You could tho.

To turn it off, give it whatever you consider a zero signal.

We did one project with Bellofram analog regulators. They worked OK and we had to get the true off option (so it doesn't leak air) Since then, I have been using SMC EtherNet/IP regulators. Those are nice.
  Reply With Quote
Old March 12th, 2018, 03:19 PM   #3
EricBig
Member
United States

EricBig is offline
 
Join Date: Mar 2018
Location: usa
Posts: 21
Quote:
Originally Posted by padees View Post
You will need an analog output card to control the regulator. Just power it up with DC, don't have to go thru the PLC for power supply. You could tho.

To turn it off, give it whatever you consider a zero signal.

We did one project with Bellofram analog regulators. They worked OK and we had to get the true off option (so it doesn't leak air) Since then, I have been using SMC EtherNet/IP regulators. Those are nice.
But if u look at page 3 in the specs. At the right side it tells me a DC common & command
Are u sure to use analog out?
  Reply With Quote
Old March 12th, 2018, 03:31 PM   #4
Mickey
Lifetime Supporting Member
United States

Mickey is offline
 
Mickey's Avatar
 
Join Date: May 2003
Location: Palmdale,Ca
Posts: 10,145
Please provide the complete model number for your valve.
__________________
Mickey

If you want happiness for an hour-take a nap. If you want happiness for a day-go fishing. If you want happiness for a month-getmarried. If you want happiness for a year-inherit a fortune. If you want happiness for a lifetime-help someone else.
----- Chinese Proverb
  Reply With Quote
Old March 12th, 2018, 03:32 PM   #5
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,981
Quote:
Originally Posted by EricBig View Post
But if u look at page 3 in the specs. At the right side it tells me a DC common & command
Are u sure to use analog out?

Do you have a 3-pin or 5-pin model?

Looks like the 5-pin model adds the option for analog feedback which would be an analog input to the PLC. This is in addition to the power and the 4-20mA PLC output you will need to power and command the valve.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old March 13th, 2018, 12:36 PM   #6
EricBig
Member
United States

EricBig is offline
 
Join Date: Mar 2018
Location: usa
Posts: 21
Quote:
Originally Posted by OkiePC View Post
Do you have a 3-pin or 5-pin model?

Looks like the 5-pin model adds the option for analog feedback which would be an analog input to the PLC. This is in addition to the power and the 4-20mA PLC output you will need to power and command the valve.
OkiePC: Yes so, i connected my air valve to my analog output card#1769-OF4/A its a compact logix.
and created 5 tags
1- MAX_PSI ->100
2- MIN_PSI -> 0
3- MAX_Engineering_Unit -> 20,000
4- MIN_Engineering_Unit -> 4000
5- Data_Input_PSI -> my controlling input

now could you please confirm if my formula is right or what i am missing please?

=> [100/(20,000 - 4000)] = 0.00625
=> 0.00625 x Data_Input_PSI = output in PSI to control my air valve.

Is that correct?
  Reply With Quote
Old March 13th, 2018, 12:58 PM   #7
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,981
Quote:
Originally Posted by EricBig View Post
OkiePC: Yes so, i connected my air valve to my analog output card#1769-OF4/A its a compact logix.
and created 5 tags
1- MAX_PSI ->100
2- MIN_PSI -> 0
3- MAX_Engineering_Unit -> 20,000
4- MIN_Engineering_Unit -> 4000
5- Data_Input_PSI -> my controlling input

now could you please confirm if my formula is right or what i am missing please?

=> [100/(20,000 - 4000)] = 0.00625
=> 0.00625 x Data_Input_PSI = output in PSI to control my air valve.

Is that correct?
I'm lost on that last part. If you want 100 psi, you will need the output data to be 20000. But if you set up the card to do the scaling for you, you just need to populate Data_Input_PSI with a value of 100.

If you are rolling your own scaling formula (which I think is the case)

You will want to compute the raw data as Data_Input_PSI/MAX_PSI*(MAX_Engineering_Unit-MIN_Engineering_Unit)+MIN_Engineering_Unit

This assumes MIN_PSI will always be zero. Also, I disagree with your naming of the MIN and MAX Engineering units, that should be called MIN_RawData and MAX_RawData or something...It isn't really engineering units.

I may have misunderstood what you're doing, so let me know if that is the case.
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old March 13th, 2018, 01:17 PM   #8
EricBig
Member
United States

EricBig is offline
 
Join Date: Mar 2018
Location: usa
Posts: 21
Quote:
Originally Posted by OkiePC View Post
I'm lost on that last part. If you want 100 psi, you will need the output data to be 20000. But if you set up the card to do the scaling for you, you just need to populate Data_Input_PSI with a value of 100.

If you are rolling your own scaling formula (which I think is the case)

You will want to compute the raw data as Data_Input_PSI/MAX_PSI*(MAX_Engineering_Unit-MIN_Engineering_Unit)+MIN_Engineering_Unit

This assumes MIN_PSI will always be zero. Also, I disagree with your naming of the MIN and MAX Engineering units, that should be called MIN_RawData and MAX_RawData or something...It isn't really engineering units.

I may have misunderstood what you're doing, so let me know if that is the case.

Yes i believe you are totally right for the name tags.
and Yes i need to run my own formula to control the PSI
that been said with your formula as follow.

Data_Input_PSI/MAX_PSI*(MAX_Engineering_Unit-MIN_Engineering_Unit)+MIN_Engineering_Unit

which will equal to:[[X(input) / 100] * [20,000 - 4000) + 4000]

Is that what you mean?
  Reply With Quote
Old March 13th, 2018, 01:26 PM   #9
OkiePC
Lifetime Supporting Member
United States

OkiePC is offline
 
OkiePC's Avatar
 
Join Date: Mar 2005
Location: ENE of Nowhere Oklahoma
Posts: 9,981
Quote:
Originally Posted by EricBig View Post
Yes i believe you are totally right for the name tags.
and Yes i need to run my own formula to control the PSI
that been said with your formula as follow.

Data_Input_PSI/MAX_PSI*(MAX_Engineering_Unit-MIN_Engineering_Unit)+MIN_Engineering_Unit

which will equal to:[[X(input) / 100] * [20,000 - 4000) + 4000]

Is that what you mean?
Yes, so plug in some numbers to check:

If you want 50psi, you will have:
(50/100)*(16000)+4000 = 12000 (12 milliamps)
__________________
It's not all the variables I am most concerned with, it's the undiscovered constants.
  Reply With Quote
Old March 13th, 2018, 01:33 PM   #10
EricBig
Member
United States

EricBig is offline
 
Join Date: Mar 2018
Location: usa
Posts: 21
Quote:
Originally Posted by OkiePC View Post
Yes, so plug in some numbers to check:

If you want 50psi, you will have:
(50/100)*(16000)+4000 = 12000 (12 milliamps)

I really appreciate your help.

Thank you so much
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Calculation of compressed air to valve actuators joaco1993 LIVE PLC Questions And Answers 8 August 22nd, 2016 05:59 AM
Solenoid Air Valve and Solenoid Vacuum Valve Tofo LIVE PLC Questions And Answers 11 October 26th, 2013 10:33 PM
What type of Pneumatic Valve to Inflate and Deflate Air Spring ( Air Bags) Quickly Rob S. LIVE PLC Questions And Answers 5 May 3rd, 2013 09:54 AM
Safety question. How does a 5/3-way pneu valve behave when air is off ? JesperMP LIVE PLC Questions And Answers 22 November 9th, 2009 07:38 AM
PID for proportional air valve Alex Pel LIVE PLC Questions And Answers 17 June 21st, 2007 02:59 PM


All times are GMT -5. The time now is 08:44 PM.


.