Air valve
You will need an analog output card to control the regulator. Just power it up with DC, don't have to go thru the PLC for power supply. You could tho.
To turn it off, give it whatever you consider a zero signal.
We did one project with Bellofram analog regulators. They worked OK and we had to get the true off option (so it doesn't leak air) Since then, I have been using SMC EtherNet/IP regulators. Those are nice.
But if u look at page 3 in the specs. At the right side it tells me a DC common & command
Are u sure to use analog out?
Do you have a 3-pin or 5-pin model?
Looks like the 5-pin model adds the option for analog feedback which would be an analog input to the PLC. This is in addition to the power and the 4-20mA PLC output you will need to power and command the valve.
OkiePC: Yes so, i connected my air valve to my analog output card#1769-OF4/A its a compact logix.
and created 5 tags
1- MAX_PSI ->100
2- MIN_PSI -> 0
3- MAX_Engineering_Unit -> 20,000
4- MIN_Engineering_Unit -> 4000
5- Data_Input_PSI -> my controlling input
now could you please confirm if my formula is right or what i am missing please?
=> [100/(20,000 - 4000)] = 0.00625
=> 0.00625 x Data_Input_PSI = output in PSI to control my air valve.
Is that correct?
and created 5 tags
1- MAX_PSI ->100
2- MIN_PSI -> 0
Is that correct?
I'm lost on that last part. If you want 100 psi, you will need the output data to be 20000. But if you set up the card to do the scaling for you, you just need to populate Data_Input_PSI with a value of 100.
If you are rolling your own scaling formula (which I think is the case)
You will want to compute the raw data as Data_Input_PSI/MAX_PSI*(MAX_Engineering_Unit-MIN_Engineering_Unit)+MIN_Engineering_Unit
This assumes MIN_PSI will always be zero. Also, I disagree with your naming of the MIN and MAX Engineering units, that should be called MIN_RawData and MAX_RawData or something...It isn't really engineering units.
I may have misunderstood what you're doing, so let me know if that is the case.
Yes i believe you are totally right for the name tags.
and Yes i need to run my own formula to control the PSI
that been said with your formula as follow.
which will equal to:[[X(input) / 100] * [20,000 - 4000) + 4000]
Is that what you mean?
Yes, so plug in some numbers to check:
If you want 50psi, you will have:
(50/100)*(16000)+4000 = 12000 (12 milliamps)
So if I want to see when the air valves open and close on a screen on the HMI is all that needs to be done is to address the bit with the address...
19
3,314
Hello Experts, I am going to be integrating an AI module into an existing panel and wants to know what should be measuring range setting when i...
1,886
Hi ! , not sure if anyone here knows how to calculate this.. but just in case ; I will instal a cluster of 20 valves and have to calculate the...
4,689
May I know whether they are the same thing? Can I use a regular Solenoid air valve to gate vacuum?
4,726
I am building a machine , and I have 3 Air Springs ( Air Bags ) that need to Inflate and Deflate very quickly. What type of valve do you recommend...
3,199